Volt Drop Calculation with Auto transformer
Calculating volt drop at say 6Kv bus, with 126MVA, and a motor rating of 7.7Mw 6Kv FLC 832A and starting current of 4401 a ( Is/In 5,29) and volt drop on 6kV net not to exceed 15% then on DOL we get 27% drop.
So if we introduce a auto transformer with a rating of 9MVA, impedance of 6% and say 70% tap, do we calculate the volt drop with the motor Is / In of 5.29, or do we calculate with Is / In 2.6 ( 0.7 x O.7 x 5.29 )
RE: Volt Drop Calculation with Auto transformer
The voltage is reduced to 70% so the current is also reduced to 70%.
The torque the motor produces drops by 0.7 x 0.7
In reality, the starting voltage drop will lower the current even further but it's a safe first approximation to ignore this effect.
Do make sure the motor still produces enough starting torque with the lower voltage though. If you use the 70% tap and drop the source voltage 15% then you will be applying 55% of rated voltage to the motor. This means the motor produces 0.55 x 0.55 = 0.3 = 30% of it's full-voltage starting torque. Lowering the starting torque that much means the motor may stall before it reaches full speed.
The current drawn from the supply is what you need to woprk with.