×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Secondary concentric neutral terminations

Secondary concentric neutral terminations

Secondary concentric neutral terminations

(OP)
Hey all,

Had a question regarding concentric grounding terminations.  We have a 138 - 25 kV delta-Yg power transformer feeding 25 kV switchgear via 3 circuits of 25 kV - 750 kcmil triplexed cable with concentric neutrals on each phase.  Our standard is to have the concentric neutral tied to the power transformer (at X0 which is tied to the ground grid), and leave it disconnected at the switchgear end.  This would prevent circulating currents through the concentric neutral.  However, I was thinking that any unbalanced current would instead flow through the ground grid to return to the transformer, which doesn't really make sense to me.  I am curious to know what others are doing in this type of installation (tying the concentric neutral at the switchgear end or not).  Why is one better than the other?

Thx,
Pete

RE: Secondary concentric neutral terminations

If you are covered by the NEC there are prohibitions against using only earth as a ground return path.  I believe there are similar in the NESC.  You need to tie your concentric neutral to the neutral bus at the switchgear end.  Why, oh why, would you spend the money for concentric neutrals and then not connect them?  If you only need three phases, just use shielded cable and run a 600V insulated ground conductor, but you need a conductor as a path for ground fault return.

RE: Secondary concentric neutral terminations

Assuming the concentric is rated for the fault current (I'm guessing you have concentril rated for at least 1/3rd neutral with the triplexed 750) you connect it at both ends.  What happens if you have a ground fault in the switchgear?  You want the concentric to carry the fault current back to the power transformer.  The only time you would not connect both ends is if you have tape shield which is only for shielding and is not sized to handle the fault current.  This installation is no different than any URD feeder with the same conductors.

RE: Secondary concentric neutral terminations

Another way to do it is connect the concentric screen wires to ground at one end only, but run a separate rated ground continuity conductor. This is the approach used by the company I work for. If you connect both ends you will get circulating currents in the screens. By preference I would connect the screens to ground at the switchgear end, as this is likely to be visited more by staff. Under fault conditions you will get a potential difference between the screens and the local ground at the disconnected end, and for this reason the screens should be shrouded with insulation. This applies whichever end you choose, but there is slightly more chance that staff will be at the switchgear under fault conditions than the transformer, as they may be fault switching for example.
Regards
Marmite

RE: Secondary concentric neutral terminations

I also prefer Marmite's method.

http://tinypic.com/view.php?pic=4vn0som

A picture taken of a damaged 630mm² singe-core cable due to circulating currents. The cable was installed and grounded at both ends, no-one considered circulating currents, and it was probably energized for two weeks before it blasted.
In the picture you can see the damaged cable with a Raychem cable-end (red) and a radiator-fin of the 20MVA transformer. The white thing in the right top corner is a current-limiting reactor with a piece of the 11kV busbar connected to it.

In this particular incident the expected circulating current was 280A at a load of 670A  - leaving a few people with red faces!

Regards
Ralph

Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon

Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376: Eng-Tips.com Forum Policies

RE: Secondary concentric neutral terminations

Hi.
It's not so simple. It's function of length of cable.
In short cables we grounded cable on one end ( supply end).
In case of long cables on both sides. One of the reasons is safety, on not grounded end possible HV potential because long cable capacitance.
I'll try found my old instruction about this issue and I'll send to you.
BTW, we also add grounding cable 95mm^2 between several
building and current circulate in this cable.
Regards.
Slava

RE: Secondary concentric neutral terminations

Ralph's picture is a shielded cable, not a cable with a concentric neutral.  Concentric screen and concentric neutral are two very different things.

http://www.okonite.com/Product_Catalog/section2/sheet38.html shows a concentric neutral conductor and http://www.okonite.com/Product_Catalog/section2/sheet4.html shows a shielded cable.

The concentric neutral provides the equipotential plan provided by the shield, but is also intended as a current carrying conductor.  Concentric neutrals are available in 33% rating and 100% rating.  The 33% is used on three phase circuits, where three 33% in parallel provides full capacity.  The 100% is used on single phase circuits, allowing a single phase drop to be run using a single cable.

If one is using concentric neutral cable for applications where shielded cable would work, one is spending way too much and has a cable that is much more difficult to work with than necessary.  If the concentric neutral is actually appropriate for the installation at hand, then it is imperative that the concentric neutral be connected at both ends.

Shielded cable and a separate neutral conductor can be used in stead of a concentric neutral cable, or you can run a separate neutral in parallel with a concentric neutral and then treat the neutral as a really expensive shield, connecting it at only one end.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources