Do you generally use 100 psf unreducible live loads on corridors and stairs or use 100 psf reducible LL?

RE: Stair & Corridor Live Loads

stairs - unreducible
corridors - most of the time we use unreducible.  IBC says corridors in assmebly occupancy is unreducible.  Also, offices have 80 psf load for elevated cooridors.

RE: Stair & Corridor Live Loads

IBC 1607.9.1.1 Says that you cannot reduce live loads that EXCEED 100psf.  And 107.9.1.3 Says that live loads of 100psf or less shall not be reduced in "public assembly occupancies".

I think you can interpret that as allowing a reduction as long as the area you are considering is not classified as "public assembly".  I'm not sure how you would get 100psf that wasn't public occupancy though.  I wouldn't reduce it unless you have a really good reason and can back it up.

RE: Stair & Corridor Live Loads

Usually stairs/corridors are small enough that the amount of reduction is pretty small so I don't bother with it.

RE: Stair & Corridor Live Loads

In addition to the 100 PSF uniform load, ASCE 7 also requires a 300 lb. concentrated load (distributed over 4 sq. in.) on each tread. I have always assumed that this concentrated load in NOT concurrent with the uniform load.

www.SlideRuleEra.net idea

RE: Stair & Corridor Live Loads

Corridors serving private residences or hotel rooms can be designed for the same live load as the occupancy that they serve.  This has been discussed and argued vehimently on this site before; however, that is what the code says and IMHO it is certainly acceptable.  

RE: Stair & Corridor Live Loads

ASCE 07 Section 4.3:  "Floors ... shall be designed to support the uniformly distributed live loads or the concentrated load ... whichever produces the greater load effects."

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources