Screwed Connection
Screwed Connection
Screwed Connection
Hi everybody
I need your response.
In my design spec. there is paragraph as bellow.
"Screwed connections are prohibited where threads provide the only seal of the pressure boundary."
I want to know why this requirement is applied.
And, this requirement shall be applied, is there any  code/standard that this requirement is addressed.
Best regards,
RE: Screwed Connection
The context is necessary to really evaluate the phrase.  Assuming that this pertains to piping or valves, the requirement includes flanges or welded end connections for the process connections.  Threaded ends are not acceptable.  The requirement would apply to the bonnet, another pressure containing connection.
It is common for the first valve off of the pipe to be either welded or flanged (especially in services where there is H2S present).
If you need an isolation valve, for example for a PT, the first valve may be welded or flanged, then your gauge valve, then then the PT.
Is this your contex?
"Do not worry about your problems with mathematics, I assure you mine are far greater."
Albert Einstein
Have you read FAQ731-376: Eng-Tips.com Forum Policies to make the best use of Eng-Tips Forums?
It's applied because threaded fasteners tend not to retain the pressure boundary.
That depends on the type of application (service) and the country of installation.
Patricia Lougheed
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of the Eng-Tips Forums.
Want to post an image? Look at the FAQ's in forum559: SolidWorks 3D CAD products
Quote (cityone1):
Well, to quote ASME PCC-2 2006, Article 2.3: When the convenience of a threaded connection is desired, and the reliable seal of a welded connection is required, a seal welded threaded joint is sometimes used.
Seal welding is also addressed in ASME B31.3 and probably the other B31.x codes...
jt
Sounds like the requirement eliminates NPTF joints where thread interference is the only fluid seal.  Other joints are permitted where the thread, if used, is not the pressure seal or the only pressure seal.
Ted