shear wall reinfocement
shear wall reinfocement
(OP)
hi everybody
i used ubc 79 and ACI 318-99
I HAVE DHEAR WALL IN MULTISTORY BUILDING UNSAFE FOR THE SHEAR RATIo the arch enginneer refuse to incease the width of wall
i hear we can add stuirrps in the shear wall to be safe in shear
but i do not know what is the equation to calculate that and what is the condition ?
can you help me?
i used ubc 79 and ACI 318-99
I HAVE DHEAR WALL IN MULTISTORY BUILDING UNSAFE FOR THE SHEAR RATIo the arch enginneer refuse to incease the width of wall
i hear we can add stuirrps in the shear wall to be safe in shear
but i do not know what is the equation to calculate that and what is the condition ?
can you help me?





RE: shear wall reinfocement
Either way, ACI 318-99 should not be used as it is not referenced by the earlier UBC 97.
But in ACI - see section 11.10 for shear reinforcing of walls. Specifically see 11.10.2 which refers you to Equations (11-1) and (11-2), sections 11.10.5, 11.10.6 and 11.10.9.
Hope this helps.