I am atteneding to a break-down on the differential relay(Duobias-M)for a 33kV/11kV Transformer. Existing CTs are of ration 200/1 and 600/1. I have DDT relays for use as regards the emergency. Is it possible to use the DDT relays without using interposing CTs, given that I don't have the ICTs at my disposal and the transformer is of vector group Yy0.






RE: Transformer Differantial protection
Are you sure, the transformer no load ratio is 33/11 and not 11.5 or some thing else.
If the ratio is 33/11kV, with the given CT ratios and the vector group of trafo, it should be possible to avoid ICTs provided the main CTs themselves are connected in delta on both primary and secondary (Yy0).
But, if the no load voltage ratio is other than 33/11kV, you may need ICTs for ratio correction or may have to factor the CT errors while selecting the relay pick up setting.
Trust the above is useful.
RE: Transformer Differantial protection
RE: Transformer Differantial protection
Aside from Raghun's comment:
Due to the British influence, many of the former British colonies used a combined REF and differential scheme, including interposing CTs, for transformer protection. By taking the interposing CTs away, you might loose REF-protection.
What kind of earthing method do you use on the primary side and on the secondary side of the transformer?
Regards
Ralph
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376: Eng-Tips.com Forum Policies
RE: Transformer Differantial protection
We use solid earthing. Ok, I connected the CTs in delta and managed to put back the transformer into service. Since it was an emergency I only checked for the currents in the operate and noneoperate windings on load. The next time I get an outage I will test the scheme under thruoghfault conditions. We decide to apply only the differential scheme.