Lateral sliding connection of masonry wall to steel moment frame
Lateral sliding connection of masonry wall to steel moment frame
(OP)
I'm designing a 4-story steel moment frame building with masonry walls. Masonry is outside of steel frame so CMU is not inbetween the columns. Since I'm tying a rigid CMU wall to a very flexible steel moment frame, I need a connection between the CMU and slab (or steel beam) that will allow sliding (about 1" to 1.5" at very top) parallel to the wall, but hard support perpendicular to the wall. Durowal's sliding connections are only oriented to allow vertical sliding, not horizontal. Preference would be not to use a custom built steel connection every so many feet, but it looks like that is the only way at this point. Does anyone have any suggestions?
I'm not the project manager making the final say about what system to use. Moment frame rather than shearwall was mandated due to the 1st floor from wall jutting out so the masonry wall from 2nd floor through roof rests on the steel beam line. Project is in South MS, seismic will likely control in one direction and wind in the other.
Concrete slab on metal deck on steel bar joists on steel beams. CMU is NOT load bearing, only connected for lateral.
P.S. this is a temporary account until mine is fixed, hence the name Temporary.
Thanks much.
I'm not the project manager making the final say about what system to use. Moment frame rather than shearwall was mandated due to the 1st floor from wall jutting out so the masonry wall from 2nd floor through roof rests on the steel beam line. Project is in South MS, seismic will likely control in one direction and wind in the other.
Concrete slab on metal deck on steel bar joists on steel beams. CMU is NOT load bearing, only connected for lateral.
P.S. this is a temporary account until mine is fixed, hence the name Temporary.
Thanks much.






RE: Lateral sliding connection of masonry wall to steel moment frame
Don't you have stair and lift shafts you can use to stiffen the building?
RE: Lateral sliding connection of masonry wall to steel moment frame
For the localized condition you describe this could be done with a steel angle welded to the frame with slotted holes in the direction of the frame at the CMU wall, or vice- versa.
The problem comes in trying to solve the global solution of the problem. What do you do at the corners of the building? The corner of the frame wants to move parallel to itself, but cannot as it is restrained by the CMU.
It appears that the CMU cannot be continuous around the corner, but must have a gap that allows movement in two directions.
Mike McCann
McCann Engineering
RE: Lateral sliding connection of masonry wall to steel moment frame
I think we are actually going to be able to go back to a shear wall system for this project (found out after talk with Durowal and posting this question), but it makes for an interesting bit of knowledge for possible future situations. I'll still check back to see if anyone else has any other ideas... would be interesting to see other engineer's approaches.
Thanks for the input guys.
RE: Lateral sliding connection of masonry wall to steel moment frame