Cooling capacity using water vs. 60/40 EGW

Cooling capacity using water vs. 60/40 EGW

Cooling capacity using water vs. 60/40 EGW

(OP)
Does anybody know how to quantify the performance difference when using 60/40 egw instead of water in a chiller evaporator that uses R134a refrigerant?

RE: Cooling capacity using water vs. 60/40 EGW

Performance difference may exist or may not. As far as chiller is concerned, there is no difference. If you want to get the same capacity at secondary refrigerant side, keep the same heat capacity (i.e product of mass flowrate and specific heat).

RE: Cooling capacity using water vs. 60/40 EGW

Thermal conductivity and capacity is poorer for EG.  

How cold are you going?

The mix should only have enough EG to keep the fluid from slushing, otherwise, you're simply wasting refrigerant capacity.

TTFN

FAQ731-376: Eng-Tips.com Forum Policies

RE: Cooling capacity using water vs. 60/40 EGW

Glycol is 5-10% less efficient than water in transferring heat. However, this is more than recouped by the elimination of scale, dirt, and corrosion that can reduce heat transfer!Also,
Glycol systems are usually slightly more expensive than water systems. There is a one-time initial cost to fill the system with 30-40% glycol.
Convenience - In cooling systems where components are frequently disconnected and reconnected, the glycol is typically captured and added back to the system

RE: Cooling capacity using water vs. 60/40 EGW

In adition to the above if you want to maintain the same cooling capacity as just water then at a 40% ethalene glycol solution you will have to increase the pumping capacity 14%

RE: Cooling capacity using water vs. 60/40 EGW

The Dowtherm document shows <70% specific heat of water and <60% thermal conductivity of water at 10ÂșC

TTFN

FAQ731-376: Eng-Tips.com Forum Policies

RE: Cooling capacity using water vs. 60/40 EGW

What you gain by specific heat , you loose with thermal conductivity .

RE: Cooling capacity using water vs. 60/40 EGW

Add glycols only to prevent freezing/slushing, not for corrosion protection.  You can buy corrosion inhibitor packages to add to pure water systems, at less cost than glycol, and still maintain the heat exchange performance of pure water.  Glycols by themselves are not corrosion inhibiting (and in fact glycols can decompose/oxidize to form acids that will actually accelerate corrosion); commercial anti-freeze products have the inhibitors already added in.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources