Transformer bushing spacing in oil?

Transformer bushing spacing in oil?

Transformer bushing spacing in oil?

(OP)
Hi I am refurbishing a 14.7kv three phase transformer, pad mounted and I need to find out how far to space the bushings on the secondary connection between the phases and the tank (ground). The tank is filled with oil.
I have consulted my CSA standards and have only found tables for connections in air. I have also been searching the net with no luck.
Any help or direction would be great.
thanks,
T

RE: Transformer bushing spacing in oil?

I think it is BS 162 for substations which has clearances in oil in a tabular form.

RE: Transformer bushing spacing in oil?

transformer oil is about 35kV breakdown for 1/8" gap. Most 12.47kv transformers I have seen have abourt 12" or more spacing on load break elbow bushings. More for substation style or live front.

Why would you be relocating the bushings on a refurb?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources