Cooling Towers -Indoor In-slab Sump
Cooling Towers -Indoor In-slab Sump
(OP)
Does anybody know a source of information on designing indoor buffering tanks for cooling tower water?
I found a pdf from Delta Cooling Towers about sizing the tank to store 3X the system circulation rate. Any help would be appreciated.
I found a pdf from Delta Cooling Towers about sizing the tank to store 3X the system circulation rate. Any help would be appreciated.





RE: Cooling Towers -Indoor In-slab Sump
RE: Cooling Towers -Indoor In-slab Sump
"Buffering" tanks are normally used on the chilled water side to prevent rapid load swings on chillers. I have never seen a "buffering" tank on a cooling tower. I have seen indoor and underground sumps. The underground sumps I service hold about 15,000 gallons on a 1200 ton tower.