Fire Protection Piping Design
What are the design guidelines or criteria in the design of Fire Protection Piping?
RE: Fire Protection Piping Design
You need to look at NFPA 13 for above gound piping and NFPA 11 for undergound piping.  If you are out buying NFPA books you may want NFPA 30 and NFPA 35 while you are at it.  They deal with flamable liquid handling.
Goodluck
Stonecold
The original poster was Pmover.
NFPA 11    Standard for Low-, Medium-, and High-Expansion Foam  2002 Edition
 NFPA 11A    Standard for Medium- and High-Expansion Foam Systems  1999 Edition
 NFPA 12    Standard on Carbon Dioxide Extinguishing Systems  2000 Edition
 NFPA 12A    Standard on Halon 1301 Fire Extinguishing Systems  1997 Edition
 NFPA 13    Standard for the Installation of Sprinkler Systems  2002 Edition
 NFPA 13D    Standard for the Installation of Sprinkler Systems in One- and Two-Family Dwellings and Manufactured Homes  2002 Edition
 NFPA 13E    Recommended Practice for Fire Department Operations in Properties Protected by Sprinkler and Standpipe Systems  2000 Edition
 NFPA 13R    Standard for the Installation of Sprinkler Systems in Residential Occupancies up to and Including Four Stories in Height  2002 Edition
 NFPA 14    Standard for the Installation of Standpipe, Private Hydrant, and Hose Systems  2000 Edition
 NFPA 15    Standard for Water Spray Fixed Systems for Fire Protection  2001 Edition
 NFPA 16    Standard for the Installation of Foam-Water Sprinkler and Foam-Water Spray Systems  1999 Edition
 NFPA 17    Standard for Dry Chemical Extinguishing Systems  2002 Edition
 NFPA 17A    Standard for Wet Chemical Extinguishing Systems  2002 Edition
 NFPA 18    Standard on Wetting Agents  1995 Edition
 NFPA 20    Standard for the Installation of Stationary Pumps for Fire Protection  1999 Edition
Sorry
It should have been "NFPA 24 Installation of private service mains and their appurtenances" for the underground items