Can 15A rated general duplex receptacles (the device) be used on a 20A breaker protected circuit fed by #12 romex?

RE: Residential Branch Circuit

I can't imagine how it would be legal... but it would work... right up until someone tried to pull 20A from the outlet for any length of time.

Dan - Owner
http://www.Hi-TecDesigns.com

RE: Residential Branch Circuit

If you switched the breaker to a 15A, you'd be fine, otherwise not legal.

Couldn't you just use a dual-purpose 15A/20A receptacle?  Ones where you can fit both the (||) and (-|) plugs into?

RE: Residential Branch Circuit

(OP)
Interestingly enough I was looking through NEC today and found that 210.21(B)(3) lists 15 or 20 amp rated receptacles as acceptable on 20 amp branch circuits serving multiple oulets.

Am I reading this wrong?

RE: Residential Branch Circuit

ktvoliver is correct, 15 amp receptacles CAN be used on a branch protected at 20 amps and using #12 Cu wire. It's been that way since at least 1950, the oldest code book I have.

Steve Wagner

RE: Residential Branch Circuit

yep, thats how it is in my master bedroom..
multiple 15A receptacles on a 20 amp circuit.

and its only a 20 Amp circuit because the electricians ran out of 14 awg wire and used 12 awg and the inspector caught it and made them put in the 20A breaker instead of replacing the wire.

RE: Residential Branch Circuit

There is no code supporting the replacement of the 15 amp breaker in mcgver's case. The 15 amp breaker met all code provisions.

Steve Wagner

RE: Residential Branch Circuit

You can always use thicker wire for a specific sized breaker, just not the other way around.  The inspector requesting that a 20A breaker be on the circuit simply because 12 gauge was used seems odd...

Dan - Owner
http://www.Hi-TecDesigns.com

RE: Residential Branch Circuit

I thought it was ridiculous too (but its North Carolina so Im not suprised). It actually delayed me moving in because the electrician couldn't get to it immediately (so I was told).
I wasn't aware of the reason until after it occured (and I moved in) or I would have given the inspector a lesson in NEC codes.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources