Structure Lightining Protection

Structure Lightining Protection

Structure Lightining Protection

(OP)
Hi,
I have this lattice incoming structure terminating a 69 KV line in to a small substation yard.

For the lightning and shielding analysis, I want to protect the equipment. Could you advise any link that could just guide me in this direction. the height of the structure is 8 meters and the yard is 10X20 m.

I think some kind of lightning rod will be required on the structure.
Thanks

RE: Structure Lightining Protection

For typical substation, you might have to use either a spherical method if you use a mast or a shielding method if you use a shielding wire.


You can find these details at IEEE Std for shielding of substation.

There is another link that might help:

www.pserc.org/ecow/get/generalinf/presentati/psercsemin1/psercsemin0/sen_2001.pdf

but I wonder for a small substation, like you mentioned a kind of lighting terminal or rod that might work as well.

There are other Gurus here who might put a word. Mast or shielding wire might be to much specially if you have only one structure.

RE: Structure Lightining Protection

IEEE 998-1996
IEEE Guide for Direct Lightning Stroke Shielding of Substations

Normally, you would have a shielding mast (just a steel pipe) mounted at the top of each column of the lattice structure.  On a small substation, if you follow the method to calculate the probability of failure in IEEE 998, you will find that the probability will be very low without any protection.  I'd say put a 10' pipe on each column (on top of a pyramid shaped top), do the IEEE 998 rolling sphere  and probability calculations to show a lower than 1 in 100 year probability of flashover, and be done with it.

RE: Structure Lightining Protection

NFPA 780

RE: Structure Lightining Protection

Yeah, what peebee said.

The most helpful analogy for lighting protection (for me) was when someone talked me through the rolling globe analogy.

The lower limit of a sphere is positioned at air terminals.  Any structure below the sphere is covered.  Any structure or equipment that intersects with the sphere is in trouble.

I can't remember the diameter of the sphere off the top of my head -

RE: Structure Lightining Protection

looks like its covered in that IEEE 998 reference if you want to look further ..

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources