Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

(OP)
Hi there, I am a little bit of a dillema, I am tring to set up an Ion 7350 power meter (from Schnieder Electric), and not haveing any luck. I have verified that all of the connections and settings are correct, and I am running it in the delta configuration. Now comes the problem: When I am metering the line I am getting strange readings, both the voltage readings and the current readings are bang on, but the power factor is out to lunch. There are 2 - 1500HP 5Kv motors connected as the load to this circuit, when they are running with no load on them they are running at a PF of approx in the range of 0.2 to0.3 and when they are under load they will run with a PF in the range of -0.2 to -0.3. I have come up with what I think to be the solution: The PT's that I am using are on the HV side of a 13.8Kv/4160V Wye-Delta Transformer, and the CT's are on the LV sid eof the transformer, and there is a phase shift of 30 degrees across the transformer. If I were to put in a 3 phase delta-Wye 1:1 120v transformer, it should restore the proper phasing, hence fixing my problem. Please let me know if any of you have heard of anyone metering like this, or if you have an more suggestions, or if you think my plan will work. Im all ears.

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

I suspect the kW readings are incorrect as well.

You're correct that the delta-wye phase shift is throwing off the metered data.  

You may be able to configure the Ion meter to compensate for this internally, but it probably won't be fun.  I would contact the Ion folks to see if it is possible.   I have found these meters to be somewhat complicated to configure.  

The aux PTs would also solve the problem.  

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Hello,

Connecting like this is like connecting to the LV side, but chosing the wrong configuration.

I suppose that you can select different configurations, like wye or delta. The one you have now corresponds to a wye connection (delta plus 30 degrees for voltage, and wye for currents = wye for both). Have you tried that setting? You may need to re-orient your CT:s to get a decent PF.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Your method sounds reasonable for monitoring purposes if the right ratios are entered into the meter. If for revenue, your transformer losses are not fully included or excluded using this method.

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Hi JeffM123.
Please contact to ION support, as DPC saied.
I worked with this support several times, good team and good company.
Regards.
Slava.

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Why not just put VTs on the low side or CTs on the high side?

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Hi Scottf.
Is not so intresting :))))
I try answer instead JeffM123:
It's unpossible or it's expensive.
JeffM123, sorry, it's joke.
Slava

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Slavaq-

5 kV class VTs cost about $350/each. That's not so much more than a 120 V Aux VT, and would make the metering much better. The ION meter can handle xfmr loss correction if the metering needs to be converted to the high-side equivalent.

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Hi Scottf.
For me it's clear add VT on LV side or CT on HV side.
My joke is only 50% joke. In many cases we are electrical Eng. locking for some "cheaper solution" instead right technical solution. ( I'm sure lot of them have same problem
, problem is $).
BTW, I'm not sure that ION7350  have xfrm losses correction.
I think are 8400-8600 or 7500-7600.
BTW, this correction work with good accuracy.

I think split toroid CT on HV side ,more or less have same price.
Regards.
Slava

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

(OP)
For information purposes, we have to do this on a hot circuit, and it is not possible to move either the PT's or the CT's, without an outgae.  As an outage is not a possiblility at this point in time I am looking for alternative methods of correcting this problem, and the aux PT's seem to be the best solution thus far.  I thank all of you for your help and sugestions.  

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

Isn't it possible to do what I said? Configure for wye instead of delta. That takes care of the 30 degree problem introduced by the D/Y transformer.

Or didn't it work?

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Power Metering with HV PT's and LV CT's on a WYE-DELTA Transformer

O.K.
JeffM123:
1. Try recommendation of Gunnar.
2. If it's not help and you need only meterig option (not kWh and kVarh), use
math option of ION7350 for visualization on dispaly.
For this you need ION Setup SW ( free of charge) and comm cable.
If you put today aux PT as temp. solution, you don't change
this connection in future.
Regards.
Slava

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources