voltage transformer
voltage transformer
(OP)
Hi, we have a VT thatsits on top and plugs into the incomer on a 33KV switch board. The nameplate says ratio 33000/110v,
and VA Phase - 200. There is 3 ht fuses feeding transformer marked A,B,C,N . My question is, 200va per phase seems quite small if I = P/V (200VA/110V)for secondary as the transformer itself physically looks quite big.Do you think i am reading it right,not much experience on the big stuff!
and VA Phase - 200. There is 3 ht fuses feeding transformer marked A,B,C,N . My question is, 200va per phase seems quite small if I = P/V (200VA/110V)for secondary as the transformer itself physically looks quite big.Do you think i am reading it right,not much experience on the big stuff!






RE: voltage transformer
It's OK, standard VT 33000/110V 200VA.
You reading is right.Don't worry.
Good Luck.
Slava