Hello
Could somebody tell me how can I modelised a VFD in SKM?

Thank you
Cristian

RE: SKM modelisation

What type of VFD (how many quadrants), does the VFD have bypass contactors, and do you have the DC module for SKM?

RE: SKM modelisation

(OP)
Unfortunaty I don't have more information about VFD (it's a GE).
Yes, I have a DC module in SKM.

Thanks

RE: SKM modelisation

Well, you could model it in SKM as a rectifier, a DC bus, and an inverter.  But without good information on the VFD you'd still be out of luck.

If it has a bypass contactor, I'd just ignore the VFD for fault calculations.  If there is no means of bypassing the VFD and the VFD can not feed back into the line, I'd just ignore the motor for fault calculations.  With a four quadrant drive you might get some fault current back out but not as much as the motor itself would produce.  I don't really know what a four quadrant drive does during faults, you might well not get any fault contribution.

So, with bypass contactor ignore the VFD for fault calculations and without bypass contactor ignore the motor for fault calculations.  For load flow you need to account for the VFD losses as well as the motor loads.  Beyond that it really depends on what you are trying to get out of your model.

RE: SKM modelisation

(OP)
Thank you very much!
I will try to modelise all posibility and I will analyse the results.

RE: SKM modelisation

(OP)
I want to find the Arc Flash - Incident energy, working distance and PPe category.

RE: SKM modelisation

Most VFDs will shut down their output almost instantaneously (much faster than the instantaneous of a breaker) for faults on their output.  I would expect that there would be very little incident energy on the output side of a VFD (without bypass contactor).  On the input side the VFD won't make any difference.

RE: SKM modelisation

(OP)
Thank you very much for your answers.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources