Allowable Bearing Press VS Structural Load
Anybody know exactly how structural engineers interpret a allowable bearing capacity from a geotech?
It really is whatever the geotech report says, in my case, the allowable bearing pressure (for shallow footings) is dead load plus design live load (or: dead load as is + (design factor)x(live load) ).
It seems I am answering my question, however, on a project that I got feedback, I am seeing that the structural engineer is considering my allowable as only dead plus live. Is this just a judgement call on the structural engineer? - maybe because the difference between (dead + live) and (dead + design live) is small? So I am asking what the general consensus is prior to pointing it out.
Thanks.
Thanks.
RE: Allowable Bearing Press VS Structural Load
f-d
¡papá gordo ain’t no madre flaca!
SDL + SLL = STL
No safety factors are on these loads. They are directly calculated loads and as fattdad states, we take the STL and divide by the allowable pressure and get a required area of footing (to put it in simple terms).
In some cases the allowable pressure is a net pressure, sometimes gross pressure.
Some cases, I have geotechs saying the pressure is for SDL plus 1/2 SLL. I don't see that too often and I'm not sure why it's done as we (the structural engineers) usually are already taking care of live load reductions in our calculations.
I've never ever added a factor to my live load and used it with a provided allowable design pressure.
The question becomes just how the bearing surface will deform under this transient load. Is it reasonable to allow the bearing pressure to go from the net allowable load (let's say 3,000 psf) to 4,000 psf as the foundation soils react against a wind gust? From this perspective there can be some live loads that are reduced. Live loads related to files, furnature, etc. are a different story.
f-d
The allowable bearing capacity must then be considered with respect to the service requirements of the foundation - such as limiting settlements or limiting differential settlement or for other reasons. In such cases, a different allowable pressure may govern - such as if one determines the settlement under the allowable bearing capacity to be 40 mm but the structural requirements limit the settlement to only 20 mm. Then the allowable pressure must be reduced in order to achieve more stringent maximum settlements than the allowable bearing capacity will cause. The reduced allowable pressures then become the allowable bearing pressures (contrast to allowable bearing capacity). The permitted bearing pressures are less than the actual capacity.
With respect to allowable bearing pressures, they are almost always (but not always) net allowable bearing pressures since the the settlement is caused by pressures exceeding the pressures already having been placed on the soil in the past. In the case of loading overconsolidated soil, though, this is not the case since the point of the existing overburden pressure to the "past" overburden pressure causes recompression settlement. Normally this is inconsequential but there are some structures where this might be more accutely considered.
I hope that this helps set out the basic difference between allowable bearing capacity and the allowable bearing pressure.
So you would typically allow a 33% increase for allowable bearing capacity, but not for allowable bearing pressure? Is that an accurate statement?
Also, one might assume all geotech's do not necessarily use the same terminology as you. That being the case, is this (in your opinion) something that should be discussed with the geotech for every project?
The language in the geotechnical report should inform the structural engineer as to what the limiting factor is - settlement, stability or strength - regardless of the terminology used.
It is a fact that some of us (myself included) can be inconsistent (or even mistaken) about the terminology, and BigH has presented the subtle distinction between allowable bearing pressure and capacity well. If you have a question or concern related to the geotechnical report, you are well within your rights and responsibilities to query the geotechnical engineer to clarify your understanding of the content of the report.
If you work with a geotech on a regular or ongoing basis, you also can have the opportunity to influence the standard report language used, and help us poor geotechs stay on the path of righteousness and more consistent terminology.
Jeff
http://www.swijetty.com
Sea Water Intake and Jetty Construction
If wind is minor, then I would not check it in detail except for overturning and uplift. Bearing pressure would then be dictated by DL + LL.
If wind is a major design criteria (such as for a billboard sign) I would try and keep the total WL + DL within the allowable bearing pressure.
I would only go into the 33% increase if I had problems meeting the design intent.
csd
I wouldn't factor the LL for check for bearing pressure conformance. I would factor the LL when designing the footing - but then I would factor the DL also.
Were you asking if the LL should be reduced or increased? It should not be reduced unless adding in wind (if required), and should not be increased unless doing strength design (but again, then you must increase DL also - not just LL).
COEngineer-
I think the 40psf is likely the max they would expect it to achieve, but is not factored. If you do strength design, you must still factor it. Also, I know I have some pretty heavy furniture in my bedroom, living room, and sunroom, but I agree that 40psf is relatively hard to achieve.
As for the terminology, I think that most standard texts use the same philosophy but perhaps worded slightly different although I have seen a few (Vargese, for instance (a good Indian text - and I reiterate a good one) where he mistakenly, in my view, does not make the distinction. This is a topic of terminology that creates so many problems - I hope that someone finally get geotechnical engineers - and especially book/paper writers on the same page.
Isolated footing: Area of footing:(LL+DL)/allowable bearing pressure
For continuous footing I do same method as above unless it is a basement wall. Usually the toe pressure control due to equivalent liquid pressure. I do not factor the equivalent liquid pressure nor the gravity live load.
When I design the reinforcement of the concrete however, I do factor the moment.
What happens if Column B has a higher load than A (the one with the highest LL%)?
Doesn't this also lend itself to possibly truly having a different footing size at each column? Do you do any design smoothing to minimize the number of footing sizes?
as far as the mention of the live load reduction by 1/2 above, my philosophy on it is that the likelyhood of all the live loads acting for long periods of time is slim (most of the time) thus the settlement analysis should account for this to some degree to keep from over-compensating. keep all the dead and at least 1/2 of live. if the scenario happened to have live loads experienced for longer periods of time, the reduction would not happen. others may have different opinions.
the recent Eurocodes (particularly Eurocode 7) have thoroughly reviewed the loads issues, building up a pretty interesting system.
There are many "load scenarios" in function of live loads, environmental loads, seismic loads, accident loads and so on.
There are coefficients which make up for the small likelyhood of two or more unfavourable conditions occurring. Many problems discussed above are worked out that way.
The system at first is not straightforward and takes soem time to get familiar with. Similar to LRFD.
I find these second-generation foundation loads interesting to evaluate.
f-d
We just design for the allowable pressure given in the geotech - at least I have never had any of the project engineers I work with as me to do anything along those lines. I have only been asked to size the footings not to exceed the allowable pressure.
I have designed some REALLY BIG footings. I am talking about 45'long x 12'wide x 3'thick combined footings with shearwalls, and columns on them. Should any additional analysis have been done on these types of footings?
i recently looked at a 30' tall CIP wall. the wall itself didn't scare me but the 30' of new fill going to be placed behind the wall after it would be built did. to make it more complicated, the ends of the wall stopped at the toe of the slope (the wall made sort of a Z shape with the end of the leg being at the toe of the slope). did some borings, lab testing, settlement analysis, etc...came out with 9" at the worst spot and <1" at the toe of the slope less than 100' away. the area was going to have to be surcharged. the architect kept telling me that he didn't have time to wait for surcharging. i told him to either follow our recommendations, don't follow our recommendations with possible severe consequences, design the thing to withstand bigtime movement, or put it on piles. so the owner made the wall go away all together since their schedule could not accomodate the surcharging/settlement monitoring program that was necessary...problem solved.
for "normal" circumstances: for a long continuous footing, we typically look at the stresses to 4B. for spread footings, we look to 2.5B. i'd call the 45'x12' closer to the spread footing or mass fill scenario. for large area mass fill scenarios, i usually end up look at the entire soil profile thickness.
3ksfx5x5=75 kips
12x45x3ksf=1620 kips (i'm guessing it probably would not be this high for most cases since there would likely be other reasons for such a large footing size--resisting uplift, fuel tank, etc).
let's just say that the settlement analysis shows settlement on the order of 1% of the 2.5B depth.
5x2.5x.01x12=1.5"
12x2.5x.01x12=3.6"
say take 1/2 of each and you're looking at 3/4" to 1 3/4" settlement between the two scenarios. if you used the 200% size rule mentioned above, then a red flag would have gone up for this particular scenario if your footings were sized as mentioned.
there's a million different scenarios that could happen--so get the geotech to look at it.
for example, i recently provided a subsurface for a client to check a small building addition out in the parking lot. they provided maximum column loads of 60k. they (the architect and engineer) specified 10 borings to x-number feet deep. the depths seemed appropriate for the structure and nothing was suspect during the drilling. after completing the drilling, i was passing along preliminary information that everything looked ok for shallow foundation support with 3000psf bearing capacity. then he happened to mention the large generator (actually said "largest that CAT makes"). i told him i'd need to recheck my recommendations and asked for loaded. he also then mentioned the very large fuel tank that would accompany the generator. he made note of a meeting the following week and i invited myself because i had seen nothing of what he had mentioned and suspected i still did not know the big picture. since the structure was going to be critical to the 24/hr-365days/yr business, we began asking lots of questions. turns out, there are 5 of these generators and fuel tanks. the loading areas were large and heavy. so as it turns out, i didn't settlement analysis about eighteen different ways before he finally gave us all the information (as far as we know). we asked for this stuff up front but they provided only very minimal information. we were very close to having to re-mobilize the drill rig to do additional sampling for lab testing. luckily, we had a few samples from the project site from two previous projects. also, since this turned out to be a very critical structure to the company that also happens to have lots of money, they were going to put GAB in the upper 7 feet of the building anyway. with that, we felt comfortable with our recommendations without additional sampling.
moral of the story, help the geotech help you by providing as much information regarding the project as you can.
Thanks!! That was a very helpful explanation.
Ask or figure out the maximum and typical loads.
Run settlement analysis for the different scenarios.
Provide table with one of the columns being Max Load.
This limits the footing size.
(MaxLoad)/(All.Brng.Cap) = Max Ftng Area
Sqrt(MaxFtngArea)= B
Similar deal with continuous ftngs.
There is a reason that geotechnical reports should state limitations to the effect that, "This report is intended for the _________ project and if plans change the recommendations should be reviewed" (or something like this). If the original development is for a gas station and the proposed construction really turns out to be a multi-story office building, then the gas station recommendations may be just wrong.
f-d
"Clever of me to use my spine to break my fall like that."