I am calculating a grounding grid based on IEEE 80-2000 for a Power Plant next to a river. I read the standard but did not find any specific words about grid design near rivers.
Is there any special concerns that I should consider?
Thanks.
I am calculating a grounding grid based on IEEE 80-2000 for a Power Plant next to a river. I read the standard but did not find any specific words about grid design near rivers.
Is there any special concerns that I should consider?
Thanks.






RE: Grounding grid next to a river
RE: Grounding grid next to a river
RE: Grounding grid next to a river
RE: Grounding grid next to a river
------------------------------------------------------------------------
If it is broken, fix it. If it isn't broken, I'll soon fix that.
RE: Grounding grid next to a river
RE: Grounding grid next to a river
Soil measurements near the river are all around 14ohms.meter.
My concern is about the loading docks with gas pipes, because simulations give me dangerous touch voltages, so, should a grounding grid be buried below water surrounding the docks? That would be very expensive.
jghrist,
I am using CDEGS to model the ground grid, but I did not know it allowed to model a river. I have been searching the help but was not able to find anything. Could you please tell me how to model the river?
RE: Grounding grid next to a river
I remember from my radar days in navy and I know if their a certain amount of the above particulate (oxygen level or small particles of matter) in the water that it turns into a conductor.
Any river water would conduct electricity like any conductor.
RE: Grounding grid next to a river
You can use a horizontal cylindrical soil model. See CDEGS Help under MALT/Define Soil Types/Cylindrical Soil Layers.
There was a paper in the 2001 Users Group Meeting on the subject. The Effects of Low Resistivity Cylindrically
Shaped Soil Volumes on Grounding Systems by Y. Yang, J. Ma and F. P. Dawalibi
RE: Grounding grid next to a river
We have driven many rods near river banks and even though you would think the top soil would be good in that location and stay consistant year round it is not always the case. I should look back and get test results from the first 10' of ground rods we have installed over the last 20 years near sources of water. Very few would be near 1 Ohm for sure as I've found very few systems that can produce that low of resistacne using commong grounding practice and remain consistant year round. Not to mention most are impossible to test without totally disconnecting the system from the outside world and that leaves life safety to chance. Driving deeper rods possibly 100 feet plus and spaced apart as far as they are long gives a more consistant ground as the earth is much more stable at those depths. We also use stainless steel as it lasts much longer than copper in the ground.