Reading and Combining Protective Trip Contacts

Reading and Combining Protective Trip Contacts

Reading and Combining Protective Trip Contacts

(OP)
I have about a dozen auxilliary trip contacts for a small generator for such things as low hydraulic oil pressure, exciter diode failure, things of that nature.  These will all trip a lock-out relay (LOR) but I'd also like to get status via a PLC so there will be immediate indication of what caused the trip.  I have only one contact for each.  I see two ways to do this:

1) Auctioneer the contacts with diodes so they are segregated into PLC inputs but combined to trip the LOR

2) Read the contacts on the PLC and setup an immediate I/O scheme (essentially an interrupt) that will trigger and output that trips the LOR.

The second scheme relies on the PLC for some of the protection.  Any thoughts on a preferred method?

RE: Reading and Combining Protective Trip Contacts

We've had PLCs lock up, and would not rely on them for protection. The PLC would introduce added time. We use the diode method, selecting diodes with specs that greatly exceed the expected duty. And they're still cheap.

RE: Reading and Combining Protective Trip Contacts

I need some education here:

What do you mean by "Auctioneer the contacts with diodes..."?

______________________________________________________________________________
This is normally the space where people post something insightful.

RE: Reading and Combining Protective Trip Contacts

(OP)
controlnovice - it just means to put them in parallel through diodes on a common bus.  If you just put them in parallel without the diodes then there is no way to read the contacts individually (i.e. if one contact closes it would be seen by all discrete inputs).  In logic terms, the diodes form an OR gate.

RE: Reading and Combining Protective Trip Contacts

Here's two common layouts.  Hope this helps.



Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: Reading and Combining Protective Trip Contacts

I have never heard the word "auctioneer" used in this context, but understood by the context of the question.

Our circuits look like the second diagram above, but without the pull down resistor. The LOR coil (at the shutdown position above) has a low enough impedance that the resistor isn't required.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources