(OP)
Let's say were were doing a brief test and were not concerned about cooling or other effects on the motor.

What is the lowest frequency output available from a typical 480v 60hz-input VFD?

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: lowest frequency output available from vfd

You can command zero speed with a VFD so that would be the equivalent of 0 Hz.  The pulsing to the motor will actually vary slightly around zero but the net will be zero Hz or very near it.

RE: lowest frequency output available from vfd

Hi Electricpete

It does edpend on the VFD, some VFDs will operate right down to zero, while others switch the output off at around 0.5 Hz. I think that youwill find that the vector drives that can providetorque right down to zero Hz will give you this performance, while the V/Hz drives will tend to give no output at zero.

Best regards,

Mark Empson
http://www.lmphotonics.com

RE: lowest frequency output available from vfd

Remember that an induction motor must have slip to produce torque. If the motor is rated for full load torque 2% slip, it will need to have 2% of rated frequency to produce full torque at zero speed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources