Can anyone tell me how to calculate the heat produced (i.e. what I would have to treat thru A/C) by a 40 Hp motor starter at 480 V?

-DOUGLAS

RE: Motor Starter

Just the motor starter itself? If so, what kind of starter? Electro-mechanical or solid state (soft starter). If it's a soft starter, is there a bypass contactor?

Assuming you meant a basic electro-mechanical Across-the-Line starter with a cheap bimetal overload relay, the only appreciable heat it will produce (if sized properly) is the dissipation of the heater elements, the contact resistance and the coil consumption. Heater elements are typically about 9W per phase, so 27W. Contact resistance is typically no more that .005% of the motor power. So at 40HP worst case (although unlikely) you are at about 30kW, making your contact resistance losses be around 15W. The contactor coil consumption varies greatly between manufacturers as a percentage of each other, but not much anyway so probably a worst case scenario is around 30W there. The aggregate total is going to be probably no more than 80W dissipation if everything is sized properly.

The one big caveat is that the contact resistance varies greatly with loading once you get up to the limits of the device and based on the contact wear over time. So if your contactor is a bit under sized or is getting old it will put out a LOT more heat. That's why we say the contacts "burned up" when it quits working. The heat can get so bad as to melt the contact materials.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources