Vertical Obstruction query c/w pics
3

Vertical Obstruction query c/w pics

Vertical Obstruction query c/w pics

(OP)
I have a recreation center that has architectural sound baffling hung vertically below sprinklers. It would appear to conform to NFPA 13 sec 8.10.6.2.2 but please look at pics at
http://www.flickr.com/photos/9995775@N05/
Any thoughts?

Regards
Dave

RE: Vertical Obstruction query c/w pics

Hard to tell if good or bad from the pictures. I would look at the distance the sprinkler heads are from the curtains to the head. you can use the section cited and may look at  8.14.2  2002 edition applies to open grid but gives distances from the head to the ceiling tile

I do not think you have a problem as long as the heads are a foot or more above the curtains. The other thing is is this an assembly building?? if so are the curtains flame retardant. If not should be, and if not they may open more heads do to fire spreading from curatin to curtain. Not and FPE or designer just have feelings.

RE: Vertical Obstruction query c/w pics

You may have a much bigger problem than NFPA 13. Under the 2006 IFC requirements in Chapter 8 for interior finish and trim, such a design in both photos is most likely not permitted.

Has anyone evaluated the color panels for flame spread and smoke production or compliance with NFPA 701? Also, what is the occupany classification of the building?

I looked at both photos and I am nervous. I think these architectural enhancements violate IFC section 807.1.2 for combustible decorative materials on ceilings.

RE: Vertical Obstruction query c/w pics

lightecho

do you mind stating what you do for a living???

RE: Vertical Obstruction query c/w pics

(OP)
Thanks for both of your replies.

The building is a public swimming pool. In conversation with the Fire Marshal it appears that the 'decorative architectural baffles' were not installed as an original part of the facility, but added later. He was quite concerned about the baffles and the plastic palm trees.

I live in northern Canada (Igloo territory as it were) and standards for everything have been quite lax. We are trying to do something about that. Our company specializes in fire prevention systems (Clean Agents, CO2,  Sprinklers, Dry / Wet chem., Foam, Fire Alarm Panels and equipment, Fire safety equipment, SCBA etc.) I have found this forum to be very helpful. Thanks for your help in the past and for this also.

Regards
D

RE: Vertical Obstruction query c/w pics

These baffles need to be treated as any other obstruction located below the sprinkler deflectors. The acceptable minumum vertical distance will depend on the type of head, but will be a minimum of 18 in. regardless of which sprinkler head is used.

I would suggest that you use NFPA 13 and apply all of the applicable codes regarding obstructions beneath the sprinklers. The most pertinent is probably Section 8.8.5.2.2 "Suspended or Floor-Mounted Vertical Obstructions" which states: The distance from sprinklers to privacy curtains, freestanding partitions, room dividers, and similar obstructions in light hazard occupancies shall be in accordance with Table 8.8.5.2.2 and Figure 8.8.5.2.2.

I hope this helps.

RE: Vertical Obstruction query c/w pics

(OP)
FFP1,
Thank you for your response. The code relating to vertical obstructions as you note are the ones that concerned me. Strictly to the letter the baffles meet this code. My problem with it all was the size of the baffle and their center to center measurements of approx. 3'. And of course there are the non-sprinkler issues relating to NFPA 701 as sited by Stookey and inferred by CDAFD.

Regards
D

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources