Cable tray fill calculation
2

Cable tray fill calculation

Cable tray fill calculation

(OP)
Being new to applications utilizing cable tray, could someone tell me if it's acceptable to install multi-conductor 600V tray cable and single conductor 600V tray rated cable in the same cable tray?

If so, NEC doesn't appear to have any reference to calculating the allowable fill area for the tray when the two wiring types are mixed.

RE: Cable tray fill calculation

See NEC (2005) 392.9 (A)

RE: Cable tray fill calculation

As long as you do not exceed the capacity of the cable tray.  Any quantity and configuration of conductors is acceptable as long as they have the same insulation voltage rating, in your case 600V.  So you may combine the two.  The NEC section referenced by MCGYVR will let you calculate the fill area.

RE: Cable tray fill calculation

(OP)
In our application we are running 3 parallel runs of (phase A,B,C, and Gnd) for the power to a 700hp VFD.  Am I correct that if we space the groups of 4 cables each,  apart from each other by the 2.15 times the cable O.D., that we can use NEC table 310.20 to determine the ampacity for the phase conductors?  When the groups of 4 cables each leave the cable tray, each group will route through an individual 18 inch long conduit/nipple into the top of the VFD cabinet.

RE: Cable tray fill calculation

You didn't specify weather you are using multi conductor tray cable or single conductor cables grouped. If single conductor, yes. If its tray cable you size per B.310.3 in Annex B.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources