MP for Tinned Copper Wire

MP for Tinned Copper Wire

MP for Tinned Copper Wire

(OP)
Hi guys,

Melting point of Tin = 203
Melting point of Cu  = 1083
For earthing calculation purpose, when considering tinned-copper wire, can we take 203 degree as the maximum allowable temperature, being on safe side as the MP of Cu is high enough to sustain this temperature.

Thanks for helpful hints.

RE: MP for Tinned Copper Wire

(OP)
yes

RE: MP for Tinned Copper Wire

Depending on your particular application and the nature of the earthing system, there may be local or national standards applicable which would tell you the maximum allowable temperature rise. In the UK for example, if you are talking about substation earthing then EA Tech Spec 41-24 applies which states 405 deg C for 3 seconds based on a 30 deg C ambient. I'm sure there will be a similar ANSI spec. You would need to be more specific about the application to get an accurate and meaningful answer.
Regards
Marmite

RE: MP for Tinned Copper Wire

If you need the tin coating to protect against galvanic corrosion of buried steel structures or lead sheaths, then you should limit the temperature to the melting point of tin.  If corrosion is not a concern, you don't need the tin plating anyway and it doesn't matter if it melts off, so use the melting point of copper.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources