foundation has dynmic load
2

foundation has dynmic load

foundation has dynmic load

(OP)
hi
i have foundation for amusemnt area have dynmic load
for example 1000 kn horzontal

how i use safe programm to solve that?

some people advice me to consider that static load but after x by 2 mean the load became 2000 kn
but i doubt in that
any suggestion fom anybody

we use ACI 318-99

THANKS

RE: foundation has dynmic load

Wow, 1000 kN (100 tonnes) is a large dynamic force.  Are you sure you have your units correct?  What is the frequency of the exciting force?

Bowles' Foundation Analysis & Design is a good text for dynamically loaded foundations.

RE: foundation has dynmic load

measure or calculate the accelerations. if there is no effect of resonance, an acceleration of 2g means, yes, double the static load.

RE: foundation has dynmic load

What are the static and dynamic components of your load, and the frequency?

RE: foundation has dynmic load

(OP)
the contractor give me 1000 kn horzontal dynamic load
and give me 5000 kn static load veritacal and give me own weight

without any frequency.

RE: foundation has dynmic load

The contractor is evidently trying to cover stiffness with strength.  You can put enough rubber bands on the side of that foundation to resist 1000kn, but it won't be very stiff.  He needs to give you a driving frequency and you need a competent soils engineer to give you dynamic properties of the soils where this foundation is going.

Check Bowles' book or the Arya, O'Neil & Pincus tome "Design of Structures and Foundations for Vibrating Machines".

There is a lot to it and if your contractor is giving you loads that high, it must be a pretty serious machine...



If you "heard" it on the internet, it's guilty until proven innocent. - DCS

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources