No ac Decrement (NACD)
Could anyone provide the name and number of the IEEE document that defines NACD.  I've been through a number of books I have and have been searching the hardcopy of the IEEE C37 Book but have not had any success.  I think if I had it on a pdf I could do a search and find it.  Personally, I don't find the IEEE C37 book to be very user friendly.
Thank You
RE: No ac Decrement (NACD)
I'm pretty sure it is in ANSI C37.010, but I don't have a copy here at home.  I'll check when I get in the office later today.
Our copy of C37 seems to have grown legs, but I checked Conrad St. Pierre's book and he references C37.010 when discussing definitions of Local, Remote and NACD.
NACD is a ratio of the non-decaying ac current to the total short circuit current, per CSP's book.
Here is the closest to a definition of NACD that I can find in C37.010.  The document uses the term in several subsequent discussions, and assumes the concept is understood from this:
A.4 Derivation of E /X multipliers
Figure A.5 shows the relationship of fault current (Iasym/Isym)nacd (the subscript nacd indicates that there is
assumed to be no ac decrement) as a function of X/R for various contact parting times. This family of curves,
which considers only the decay of the dc component of fault current, forms the basis of....
If I'm understanding this correctly, then there must be a typo in Conrad's book where he references NACD as non-decaying ac current(Isym) to total fault current (Iasym)whereas C37 has it as Iasym/Isym.
I'd have to assume the definition in ANSI C37.010 is "definitive".