Generator short circuit current calculation

Generator short circuit current calculation

Generator short circuit current calculation

(OP)
Hello
For a project, I need to calculate short-circuit current calculation following IEC60909 rules.
The question is:
The generator is rated 45MVA and I have the characteristics for 45MVA. The power plant where the generator will be used is dedicated to 42MVA (active power / power factor) and I can calculate the reactance from 45 to 42.
But in my mind, for the calculation of the short-circuit current I must used the rated generator characteristics and particulary 45MVA (in the short-circuit calculation software).
Does anyone know what says the IEC 60909.
Thanks

RE: Generator short circuit current calculation

My view is that you should use the manufacturers data for the machine. Excitation Control system action will not affect the peak asymmetrical short circuit current but may affect the short circuit breaking current depending on the fault clearance time.
Regards
Marmite

RE: Generator short circuit current calculation

The generator does not care about IEC standards or how you operate the plant, so you need to use the generator's actual MVA rating.  

RE: Generator short circuit current calculation

Use the generator rating, not the rating of the combined generator/prime mover.  The initial short circuit current will be the same whether the generator is being drivn by a 45 MW turbine, a 1 MW diesel engine or is running as a synchronous condensor without a prime mover connected.

RE: Generator short circuit current calculation

I will also concur with the above responses; the machine is the machine and as long as it is spinning at synchronous speed it will have the published characteristics.

RE: Generator short circuit current calculation

(OP)
Thanks a lot for your answers. They confirm my mind.
Regards.
PB

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources