Here's the situation:

An upgrade on our equipment requires a new DC motor.  The only available spare embeded conduit is 2 x 1".  A 1" is big enough for the field leads(10AWG), but isn't big enough for the armature leads(2/0AWG).  However we could split up the field and armature leads and put one of each in the 2 1" conduits.  This would be a no-no with three-phase power due to inductive heating, but can you do it with DC motors?

RE: Field and armature wiring in same conduit?

How close are these two conduits? Nearly touching close?

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: Field and armature wiring in same conduit?

(OP)
I'd estimate 1/4 to 1/2 inch.  I'd estimate the run at about 150 feet.

RE: Field and armature wiring in same conduit?

Then off hand I can't see much of a problem.  There may be control issues someone will chip in with but the closeness of the two conduits will limit the massive B-Feild that will be created in the gap between the conduits.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: Field and armature wiring in same conduit?

There is a considerable 300 Hz (Europe) or 360 Hz (US etc) AC component in the armature current. If you are running 6-pulse thyristor rectifiers. Sometimes as high as 30 % of motor rated current. Its heating effect is actually more than a 100 % 50 or 60 Hz current. So, for same reasons that you shouldn't do it with an AC system, you should be careful here, too.

Eddy current heating is proportional to frequency squared, so your 30 % ripple at six times mains frequency will heat^.3*6^2 = 10.8 times the rated 50/60 Hz current. Even with as little ripple as 10 %, you get 3.6 times more heating.

The problem does not exist with WL sets. But I don't think youv'e got one of them. Have you?

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Field and armature wiring in same conduit?

Another possible issue is wire damage, mixing #10 AWG with 2/0 AWG in a 150 foot run may be hard on the #10s if the insulation isn't robust. Can you use something like 2 x #2 AWG  and a #10 AWG in each pipe, or 2 x #2s in each pipe and both #10s in one pipe with one set of #2s?
Phisically and code wise it depends on which type of wire you choose to use.
respectfully

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources