Question on load combinations
I am using a structural design program and I was surprised to find out that the program generated load combinations
1.  have load cases considering live load = 0. for example, if using UBC97 eq. 12-5, there are load combinatios 1.2D+1.0E
2.  When using eq 12-6 in UBC97, have load combinations like 0.7D+Rho*Eh.
Can these be right?
RE: Question on load combinations
Yes, these are similar to 0.6D+W for ASD - they consider the case of uplift.  I am surprised to see 1.2D, however, I would expect to see 0.9D.
In my UBC '97, combination 12-5 does include live load and snow, the factors f1 and f2 defined in the lower part of 1612.2.1.
I have a different equation for 12-6 than you list.  Perhaps we have different versions or updates.  Check the section again and be sure you caught everything.
it is as such : 1.1(1.2DL + (0.5 or 1)LL + E)
but the problem is how to add the "E" in this combination ... there are 16 quadratic combinations to add.
and what is meant by 1.1(0.9DL+-1.0E) the + and - in this combination for what ???
thank you
The + or - signifies that you are to take the combination that produces the worst effect.  The seismic event can occur in any direction.  So, if you consider the event in the positive X-direction and that produces a compressive force in a column, you need to also check that column-footing assembly for uplift when the seismic event occurs in the negative X-direction.
StructuralEIT
the E term in the combination " 1.2DL+ 0.5LL + E " IS FOUND TO be added linearly ??
Is it a linear combination , if yes this would cause a zero result in some cases for example moment on columns
-40-10+50= 0
plz answer
suppose we need to obtain results on a column Fx, My, Mx ...
take for example Moment around y-axis "My" @ top of the column . we observe that the dead load gives a positive moment and the seismic gives a -ve moment thus when w add the combination 1.2DL+0.55LL+E it won't give the worst case infact it will reduce the moment and all other forces.
the ubc load combinations are not purely linear they are conditionally linear ...
Am I right ?????
thanks
abdeb-
This is where the + or - comes in.  If you use -E instead of +E, you will get -40-10-50=-100, not 0.
"abdeb-
This is where the + or - comes in.  If you use -E instead of +E, you will get -40-10-50=-100, not 0."
but the combination is only +E: 1.2DL +fLL +E
there is no -E in this load combination
then reverse the direction of the seismic force and you will get an identical answer to using -E.  You have to consider the earthquake to act in either direction, not just one.
Ok , but what is meant by this combination 09DL + or - E
where the code presented the + or - condition and on the otherhand the combination 1.2DL + fLL + E presents only the +E condition???
StructuralEIT i really appreciate your posts
thanks
Only "+" E is required because E itself can be positive or negative.  To put a +/- in front of a quantity that can already be +/- in itself is redundant.  You add these quantities algebraically, so you have to consider the direction of the load, which is the +/- part.