Steel frame masonary wall connection

Steel frame masonary wall connection

Steel frame masonary wall connection

(OP)
I am working on the construction of a small warehouse builing 60' X 40'. The building is a steel framed building with masonry blockwork as the walls. I am looking for the best means to connect the steel frame and masonry blockwork, in particular the steel column masonry block wall connection or the steel beam masonry block   connection…

Thanks,
SN

RE: Steel frame masonary wall connection

I hope you're working with other experienced engineers who can help you with some company typical detsils for this.  A lot depends on what you're trying to accomplish.  For instance, if your entire lateral resisting system is the steel framing the connections are different than if the CMU walls are shear walls.

RE: Steel frame masonary wall connection

I am guessing that you are asking this simply to be able to brace the top of the wall (assuming you would have asked how to tie the diaphragm into the wall if you were concerned about getting the loads into the shearwalls).  
JedClampett makes a good point that the connection detail will be different depending on what you are trying to accomplish.  
If you are simply trying to brace the top of the wall so you don't have a cantilevered wall, we have used a bent plate welded to the WF and epoxied into the CMU.

RE: Steel frame masonary wall connection

It would be helpful to know if the roof is a diaphragm or not.  If so, a detail tying the beam to the masonry and then bracing the bottom of beam to the diaphragm is a good detail.  If it's not a diaphragm, you probably need to design the masonry to span vertically and use a wind girt near the top of the wall - I like to use Tapcon or Hilti masonry screws to fasten a girt to the masonry.  

RE: Steel frame masonary wall connection

There are many anchors out there that are suitable for attaching masonry to the steel frame.  Go to MTEK sites and look at the e-TEKS by the National Concrete Masonry Association.  They have detail and suggestions.  Remeber to put control joints in the masonry at columns.   Wire ties work well at the columns.  The top connection will be different like the others have said depending on whether you are utilizing shear walls or not.  If you are only bracing the wall, masonry anchors should do.  Check Dayton Richmond.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources