Anchor bolts after fire

Anchor bolts after fire

Anchor bolts after fire

(OP)
I have a town home project that was burned down by an arson after it was fully framed.  I haven't been to the site yet but I know that they are going to ask.  They will want to know if the anchor bolts are going to be salvagable.  What issues would you expect from bolts that have been in a residential fire?  I wouldn't imagine that the heat was very great, or at least not hot enough to alter the steel properties.  I would guess that the bolts would be okay

Any thoughts/help/ideas would be appreciated.

RE: Anchor bolts after fire

What about deterioration of the concrete in which the bolts are embeded.

If they are A36 then they may be okay but if they are high stress bolts then I doubt it.

csd

RE: Anchor bolts after fire

Was this in St. Louis??  We have had a rash of these...

I would suspect they are OK unless the sill plates turned to ash.  2x4s do a pretty good job of insulating and most of the heat should have gone up

You could always re-drill and use a drop in or Epoxy.  See Simpson or USP.

Good Luck

RE: Anchor bolts after fire

(OP)
No, this was in Arizona.  I might just have them use simpson Titan HD screws in lieu of the anchor bolts and then drill and epoxy holdown bolts for the strap holdowns (which I am sure will be useless) and then have an inspection/testing company come do a pull test on the holdown bolts that were in place at the time of the fire to make sure that they can take the uplift.

Thanks for your responses!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources