Does Open Delta Service shorten three phase motor life
(OP)
I have a proposal to install a replacement (~pump cost = $4,000) 10 Hp water pumping system which is serviced with an Open Delta three phase 240 volt 50 KW utility supply. The old system has experienced three motor burn-outs in the last 4 years. The new motor is rated at 10 Hp, 230 volt, three phase, 28 F.L.A.and has a manufacturers 5 year/10,000 Hr. warranty. I will be adding phase loss/reversal, over, under & unbalanced voltage & short cycling monitoring to the control panel. The manufacturer will honor the full warranty ONLY if "...the 230 volt/3 phase 60 Hz power source is a good dependable supply and NOT originating from an Open Delta power circuit". The utility company engineering department claims this type of service is normal and wants $5,000 to add the third transformer to the service to yield 208/120 three phase which would also require a new motor selection. We also have a small single phase lighting load. The pump manufacturer will make changes to the motor windings to accomodate the 240 Volt Open Delta supply. How much will the pump life be shortened running on an Open Delta source? Should we add our own transformer on the secondary side?






RE: Does Open Delta Service shorten three phase motor life
I suggest checking the overvoltage performance of open delta comparing with a three transformers connection including the surge protection used. This probably gives some idea of the investment, risk and guaranty issues.
Perform detail study of this system could cost more that the cost of extra transformer.
RE: Does Open Delta Service shorten three phase motor life
with an ampacity very close to the FLA of the motor.
The open delta service is very common and used often by the utilities.
RE: Does Open Delta Service shorten three phase motor life
As long as motor voltages are balanced, the motor life should not be negatively impacted. But as the load increases, the voltages out of the open delta tend to become unbalanced. This will lead to increased negative sequence currents in the motor and possible reduce the life of the motor due to higher temperature.
I'm not a big fan of open delta services for anything over about 10 hp or for anything I cared much about.
RE: Does Open Delta Service shorten three phase motor life
The reason (as was explained to me) why some pump mfrs stipulate this is that Open Delta services are usually associated with remote areas where most of the loads are 1 phase residential or farms. The problem then is, the 2 phases that the utility supplies are already at risk for wide imbalance conditions because of variable loading. When combined with an Open Delta 3 phase service which is already bordering on being unbalanced, the risk of overheating the motor is almost 100% sooner or later. The pump mfrs don't want to take a chance on the sooner side.
I did a well pump project with Open Delta service for a winery that was smack dab in the middle of a new residential development (a new trend here in California) and we put phase current monitor relays on everything, set to 30% current imbalance. We could not keep the pumps running; the relays were constantly tripping. We put a Dranetz recording meter on the utility side for 2 weeks and the two primary lines would swing 20-25% hour-to-hour at certain times of the day. We could even predict it based upon commute patterns because when people got home from work and turned down their AC thermostats, the imbalance would spike.
RE: Does Open Delta Service shorten three phase motor life
Don
RE: Does Open Delta Service shorten three phase motor life
RE: Does Open Delta Service shorten three phase motor life
RE: Does Open Delta Service shorten three phase motor life
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Does Open Delta Service shorten three phase motor life
RE: Does Open Delta Service shorten three phase motor life
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Does Open Delta Service shorten three phase motor life
Compared to a symmetrical bank of 3 transformers, the open delta bank does introduce additional unbalanced voltage to the secondary. I say additional because the circuit three phases are often unbalanced due to load and lack of transpositions. Further, the 2 transformers are frequently different sizes. There are application rules to follow so that the unbalanced voltage is better managed.
Voltage unbalance does shorten motor life simply because the motor runs hotter. Voltage unbalance produces negative sequence heating of the motor rotor. To be a significant effect, the motor would have to be running close to nameplate load. Refrigeration motors are most succeptible to shortened life from voltage unbalance. Some pump motors carry fairly high loads, so they would be affected also. For other motor applications, I don't believe you'd notice any effect on motor life.
The NEMA MG1 standard says the maximum voltage unbalance that a motor is designed for is 1%.
RE: Does Open Delta Service shorten three phase motor life
I should have mentioned that this is 10 HP submersible pump
so it is also water cooled. However, the total system cost is at $12,000 now and we do need to protect the investment as best we can.
RE: Does Open Delta Service shorten three phase motor life
If there is three-phase primary available, I'd really push for a true three-phase service. If it's V-phase, I'd do what jraef suggested and monitor the negative sequence current.
RE: Does Open Delta Service shorten three phase motor life
Can't a filter remove the issue anyway?
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Does Open Delta Service shorten three phase motor life
RE: Does Open Delta Service shorten three phase motor life
Hey, a perfect use for a VFD. On off hours, you slow the waterfall way down and save money. Or vary it like real ones vary so visitors detect variation from day to day!
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Does Open Delta Service shorten three phase motor life
Thanks again....
RE: Does Open Delta Service shorten three phase motor life
The heavy neutral current and the resulting voltage drop on the neutral would cause phase angle shifts on the system. I have had problems with phase angle shifts on three phase systems caused by heavy neutral currents resulting from severe unequal loading further downstream.
I understand that problems with open delta systems are mostly the result of neutral voltage drops on the system. I understand that open delta works well when fed from a solid, balanced system that has little neutral current.
respectfully
RE: Does Open Delta Service shorten three phase motor life
Utility is correct, no problem with open delta as long as the unbalance is within the motor's capability.
RE: Does Open Delta Service shorten three phase motor life
I have many times used VFDs on single phase but would like to hear from a VFD wizard if there are any hitches with hooking a typical VFD to open delta?
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Does Open Delta Service shorten three phase motor life
Your original open delta question has been answered. Now VFD savvy members are likely passing over this original thread not realizing there are VFD follow-ons.
I suggest you start another thread asking specifically;
Title: Powering a VFD with Open Delta
"Should I run a 10hp VFD on Open Delta 3 phase or use a higher power rated VFD and feed it single phase 240V?
What are the potential problems?"
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Does Open Delta Service shorten three phase motor life
Not meaning to espouse any one brand over another, but the Teco FM100 drive has a cool built-in timer feature with which you can directly implement the variable flow rate pattern itsmoked mentioned. I have done dozens of fountain pumps with them. You can set up 7 speeds and times, each with their own ramp up and down times of up to 60 minutes each, so by the time you run through an entire 7 cycle program, the average viewer has moved on, thinking it was entirely random.
JRaef.com
"Engineers like to solve problems. If there are no problems handily available, they will create their own problems." Scott Adams
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: Does Open Delta Service shorten three phase motor life
Thanks again... All of the responses have helped expand the range of options ...
RE: Does Open Delta Service shorten three phase motor life