UNION BEFORE THE SEALING CABLE GLAND

UNION BEFORE THE SEALING CABLE GLAND

UNION BEFORE THE SEALING CABLE GLAND

(OP)
I have seen an installation involving cables directly connected to an explosion proof enclosure via sealing type cable glands. I observed however in one occasion that there is a union between the sealing type cable gland and the explosion proof enclosure. Is this a Code violation?

I thought that the NEC does not allow any union between the enclosure and the sealing type cable gland. Further, the union may pose as a point of failure since it may create passage of combustible gas into the enclosure in the event of failure due to..say corrosion. Is there any code reference that allows this? I ask the maintenance people and they say that this union is required during maintenance works.

GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata

RE: UNION BEFORE THE SEALING CABLE GLAND

I believe there are explosion proof unions available.
respectfully

RE: UNION BEFORE THE SEALING CABLE GLAND

The NEC does not permit any fittings between a seal and a boundry point, but explosionpoof fittings are permitted between a seal and explosionproof enclosures.  

Quote:

501.15(A)(1) ... Conduit seals shall be installed within 450 mm (18 in.) from the enclosure. Only explosionproof unions, couplings, reducers, elbows, capped elbows, and conduit bodies similar to L, T, and Cross types that are not larger than the trade size of the conduit shall be permitted between the sealing fitting and the explosionproof enclosure.

Quote:

501.15(A)(4) ... Except for listed explosionproof reducers at the conduit seal, there shall be no union, coupling, box, or fitting between the conduit seal and the point at which the conduit leaves the Division 1 location.
Don

RE: UNION BEFORE THE SEALING CABLE GLAND

(OP)
Thanks Don, Waross.

GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources