% of reinforcement in column

% of reinforcement in column

% of reinforcement in column

(OP)
we cast more than 50 pediestal dimenion 700mmx700mm
with reinformcment 12 BAR diameter 16

the main problem we can not demoilish the pedital because
we fixed percast column and they fixed the beams and slab

what can i do?

RE: % of reinforcement in column

HI, swelm

Could you please more specific? i don´t now what is your problem/question. try to be more specific in tour post so we could help you

thanks

LG

RE: % of reinforcement in column

Are you saying that you have 50 columns that are about 27.5" x 27.5" with 12-#5 bars (converted to English units), which gives you a reinforcing ratio of approximately 0.5%?  Is that your question?

RE: % of reinforcement in column

If I did the metric conversions correctly, it sounds like you have about 1/2% of longitundinal reinforcing in the piers. Is this correct?

ACI has a provision to go down to 1/2% if the piers are larger than they need to be to resist the forces. What is the governing code? Does the pier, as reinforced, have enough capacity to resist the forces? Do the longitudinal bars have sufficient ties?

RE: % of reinforcement in column

(OP)
iam very sorry because i make confuse for all of you

the columns is safe  to carry the load but i notes that the % of reinforement is not enough less than 50%
we use ACI for design
the columns have ties diamter 10 mm 3 set.
my question is

is that sutiation is critial and we need repair or not ?

thanks



RE: % of reinforcement in column

1/2% is allowed if the strength is sufficient using 1/2 of Ag.  (Thus 1% of the area required is 1/2% of Ag).

RE: % of reinforcement in column

If the concern is that you're actually under 0.5%, check your design (neglecting the steel) against the ACI provisions for structural plain concrete (318-05 chp 22).  If it works as SPC, the fact that you actually have some reinforcement there is immaterial.  If the question is whether 0.5% is acceptable, above answers are correct.

RE: % of reinforcement in column

If the geometry of your pedestal matches the description of pedestal in ACI-318, then you may not need any reinforcing at all.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources