Hi

AISC has two design procedures for ponding.  One is for a case where there are flexible primary and secondary members.  The other is for when there are flexible secondary members bearing on a wall (infinitely stiff primary member: Cp=0)

What happens if you have roof joists bearing on a flexible joist girder at one end and a concrete wall panel at the other end?  Let's say the water is going to pond at the concrete wall.  Do I follow the procedure that assumes the primary member is infinitely stiff?  Or do I maybe assume the primary member stiffness (Cp) is an average of the joist girder stiffness (Cp=x) and the wall (Cp=0)...i.e. Cp=x/2.  

Thanks.

RE: ponding

I'd do your latter suggestion - run both analyses and know that you fall between them somewhere, probably half-way.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources