Tranformer Power Calculation

Tranformer Power Calculation

Tranformer Power Calculation

(OP)
The formula for an unbalanced Wye transformer output is as follows:
I(L) = SQRT[I(A)^2+I(B)^2+I(C)^2-[I(A)I(B)]-[I(B)I(C)]-[I(C)I(A)])
What is I(L)?  In a balanced Wye system, I(L) = I(Ph).  This equation given for an unbalanced Wye load is puzzling. At what location would this be measurable?

RE: Tranformer Power Calculation

(OP)
Just found the answer.  I(L) in the equ. above is to be I(N) or the current flowing on the neutral conductor.  Went back to the math and derived the equ.  The formula was posted incorrently.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources