NFPA 45 - Duct FDs

NFPA 45 - Duct FDs

NFPA 45 - Duct FDs

(OP)
I am working with the NFPA 45 code (lab ventilation). Section 6.10.3 - no fire dampers in lab hood exhaust systems. Also in 6.10.3 is an exemption describing a 'subduct' system.

We are looking at this section because we are manifolding hoods into a common riser. The riser is running in a rated shaft. Does the riser need to be run in a separate (dedicated) shaft?

RE: NFPA 45 - Duct FDs

Check the code to see if it allows you to use a seperate fire rated riser and stub the lab hood duct in to the riser with a short elbow up and no fire damper

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources