choosing proper friction rate for flex duct

choosing proper friction rate for flex duct

choosing proper friction rate for flex duct

(OP)
i am using a standard trane ductulator ,hand held slide type,and have been using an 0.1/0.2 friction rate to calculate duct size.

My issue is this,id like to find one rate to use as a standard for a rule of thumb type process and if its not the correct rate what is a good one to choose?

I am a Texas contractor and i am using r-6 flex duct in mostly residential applications..

can someone help?
TIA

RE: choosing proper friction rate for flex duct

The generally recommended
design pressure drops for residential and light
commercial duct systems are 0.10 in. w.g. for the
supply side of the system and 0.05 in. w.g. for the
return side of the system. In some cases, particularly
in light commercial systems, 0.08 in. w.g. is used for
the return side. This reduces the overall pipe sizes
in the return duct system, but also results in higher
velocities and may increase noise levels. If system
noise levels are of importance, the design pressure
drop of 0.05 in. w.g. should be used.

RE: choosing proper friction rate for flex duct

Referring to my response posted a few minutes ago

The older Hart & Cooley catalog (1995/1996)had the following title
"Flexible Duct Air friction Chart" which is now labeled on their web site as "Air Friction Chart"

Quick glance yields that the two charts are the same.

RE: choosing proper friction rate for flex duct

(OP)
thnaks i guess the .1 i have been using is the correct rate..ill use the .05 for return and see how that works..

thanks

RE: choosing proper friction rate for flex duct

If you are hanging the flex duct over rafters, or otherwise routing them so that they are not straight, then a factor needs to be applied to the friction values shown on a Ductulator or the referenced chart above.  

RE: choosing proper friction rate for flex duct

For flex duct, I would double the DP for straight duct.  Thus, if a certain size straight duct produced 0.10"/100', flex duct same size will require 0.2"/100' for same CFM.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources