Trouble finding Gas flowmeter

Trouble finding Gas flowmeter

Trouble finding Gas flowmeter

(OP)
We have an application to measure inert gas flow in a 36" duct at just under 300 SCFH. There is flammable trace dust, which also melts at about 210F. So we're concerned about using a 'hotwire-type' sensor because the dust will melt onto the heated RTD causing measurement errors. We contacted Rosemount about their annubars, but got a response saying the flow was too low; they need roughly 450 SCFH. We cannot increase flow nor reduce the duct size. Also, the R.H. is somewhere about 90%. I've heard that heated sensors don't do well with saturated streams.

Any suggestions are appreciated!

RE: Trouble finding Gas flowmeter

Check to see of the Thermo Brandt averaging pitot assembly is suitable.

RE: Trouble finding Gas flowmeter

A few ideas:

- Thermal Mass meter:  Not sure if this is what you meant about 'hotwire-type'.  It seems odd that a thermal mass meter would have a temperature that high.  But it can be affected by coatings.  http://www.us.endress.com/eh/sc/america/us/en/products/home.nsf/contentview/0E87BA0E0D8F10EDC12568CC0037B5FD

- Can you reduce the duct diameter just in the space you need to measure?  This will open the possible selection of meters.

- Target meter: Problem is accuracy and rangeability.  Unfortunately, I can't find manufacturers now.

______________________________________________________________________________
This is normally the space where people post something insightful.

RE: Trouble finding Gas flowmeter

Most thermal mass flow meters are available for use with hydrocarbon vapors.  They may use RTD or thermister elements.  Select the flow element option for the hazardous area classification that applies to the flammable dust.

RE: Trouble finding Gas flowmeter

if you only could afford a size reduction for a venturi.

RE: Trouble finding Gas flowmeter

As Mobrey products are now owned by Emerson, perhaps your Micro Motion or Rosemount peddeler may sell the Solartron products these days.

RE: Trouble finding Gas flowmeter

For low flow rates, I am thinking:
- thermal mass meters (which you already ruled out)
- annubar/pitot tube (which Rosemount already ruled out)
- turbines (which may be ruled out since you are 36" duct)
- clamp-on ultrasonic (need to determine maximum diamters)

Instead of reducing the duct, can you split the 36" duct into 4 10" ducts and then re-join? This way, you may be able to try using the turbines and ultrasonics.

"Do not worry about your problems with mathematics, I assure you mine are far greater."   
Albert Einstein
Have you read FAQ731-376: Eng-Tips.com Forum Policies to make the best use of Eng-Tips Forums?

RE: Trouble finding Gas flowmeter

Although it would be too expensive, you would need at least 13 10" ducts to achieve the same area as a 36" line.  Any solution depends on the acceptable pressure loss of the application.

I can't think of any reasonable solution.  The flow is so low compared to the duct size that it is a challenge.

RE: Trouble finding Gas flowmeter

Dryno,

I'm curious to know how you establlished the current flow rate of 300 SFCH.

Dan

RE: Trouble finding Gas flowmeter

(OP)
Many thanks for all of the input and suggestions.  As it turns out, there are two mistakes in the process data.  We (instrumentation) were given the wrong gas density.  The mass flow rate was given in PPH, so the incorrect density ( by more than an order of magnitude) resulted in grossly incorrect flow.  I compounded the problem by using units of SCFH when I should've used SCFM.  The corrected flow rate is ~17500 SCFM.  Yes, I know; that's a huge difference.

This opens up many possibilities, including mass flowmeters, if their heated wire/RTD is below 210 deg. F.  I have contacted FCI, Rosemount, and Kurz; they are working on it.  

Thanks again for your suggestions and (danw2) for questioning the data!

RE: Trouble finding Gas flowmeter

How about vortex meter?

"Do not worry about your problems with mathematics, I assure you mine are far greater."   
Albert Einstein
Have you read FAQ731-376: Eng-Tips.com Forum Policies to make the best use of Eng-Tips Forums?

RE: Trouble finding Gas flowmeter

clamp on ultrasonic

RE: Trouble finding Gas flowmeter

Are you sure your new flow rate isn't really 17500 SCFH?  Dan

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources