pole mountened transformer
pole mountened transformer
(OP)
hi every one
IS THERE ANY PROBLEM TO OPERATE A DISTRIBUTION POLE MOUNTENED TRANSFORMER WITH ALMOST NO LOAD?
if possible can any one eplaine that for me or give me a web site that could be useful
IS THERE ANY PROBLEM TO OPERATE A DISTRIBUTION POLE MOUNTENED TRANSFORMER WITH ALMOST NO LOAD?
if possible can any one eplaine that for me or give me a web site that could be useful






RE: pole mountened transformer
Slightly added electricity costs.
If been used on a relative large network with basic protection added equipment might make faultfinding more complicated - in such a case I would rather keep unnecessary equipment down.
on the other hand
I would rather keep it energized if you have problems like copper theft. Also, if oilfilled, I would rather let it be energized - it keeps the oil soaked and the moisture out.
Regards
Ralph
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376: Eng-Tips.com Forum Policies
RE: pole mountened transformer
The transformer core losses will cost money, but I don't really see any other significant concerns.