Sizing conductors

Sizing conductors

Sizing conductors

(OP)
I need some help sizing conductors for three phase.  I have a 3 phase 600A service @480V that I want to feed a machine 450' away.  Not sure the exact load yet but it will be close to that.  The calculator that I have tells me the feeder cable should be 400MCM with #2 ground.  Is this right and how can I double check this?

RE: Sizing conductors

What is the size of the breaker or fuse upstream that will be protecting the cable?  

RE: Sizing conductors

(OP)
I am not sure.

RE: Sizing conductors

Strictly looking only at conductor rating, 600 A of load at 480 V would require TWO 350 kcmil copper PER PHASE and a #1 copper ground in EACH conduit plus an appropriately sized neutral, if required.  Figure on two 3" conduits for that configuration.  This voltage drop is not a concern and that ambient temperatures are not so high as to require derating.

But you also have to consider the upstream breaker rating since it must protect the conductor.

If you have a continuous load of 600 A, your breaker will need to be 1.25 x 600 A and this requires that your conductors be larger.  

But maybe you need some consulting from a local EE familiar with these issues.  It'll be cheaper than tearing it all out and replacing it after the local inspector red tags it.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources