Is there an NEC requirement that the neutral and ground buses be completely seperate? I looked at a house yesterday that had the neutrals and grounds for the branch circuits all run to the same bus bar.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Residential Code
RE: Residential Code
RE: Residential Code
This is your 1st tie between the two.
After this, Article 250.142 gives the rules for seperating the two. 250.142(B) says "...a grounded circuit conductor shall not be used for grounding non-current-carrying metal part of equipment on the load side of the service disconnecting means..."
With a few exception, every other location will have them seperated. One exception is an existing dryer or range branch circuit. If it is a new branch circuit, it is required to have them seperated. Another exception is a panel in another building, such as a detached garage. This location may or may not have them seperated, depending on a number of things. A subpanel, or a panel that is in the same building as the main service panel, is required to have the 2 seperated, with no exceptions.
A complete reading of Article 250 of the NEC will give you the requirements.
Respectively
Rick Miell