Voltage Drop Formula

Voltage Drop Formula

Voltage Drop Formula

(OP)
I'm a fairly new engineer working for the local power company.  I have been tasked with sizing an underground run for a mobile substation.  Unfortunately, I didn't  have any power courses in college, so I have spent some time researching equations.  Can anyone provide a website or an equation to use to calculate Voltage Drop.  I have found some equations on-line, but would like to verify I'm doing things correctly.  Some information follows:
Size of mobile transformer- 35 MVA
2 conductors per phase
Conductor size- 500 kcmil, triplex
1 run of triplex in 6 inch conduit (second run of triplex in another 6 inch conduit)

I appreciate everyones' response.

Thanks

RE: Voltage Drop Formula

Here is what I use for the cable voltage drop (in %)

%VD= (KxIxZxLx100)/V

K=Phase Coefficient (2 for single phase circuit or 1.73 for three phase circuit)

I=Full Load Current (Ampere)

Z=Impedance of copper conductor(Ohms/meter)

L=Single length of conductor (Meters)

V=Source voltage at switchboard or transformer secondary (Volts)

RE: Voltage Drop Formula

In regards to the "Mike Holt" spread sheet;
The formula used appears to be based on resistance only.
You should be aware that there may be additional voltage drop due to inductive reactance. Inductive reactance is a function of both conductor size and spacing. It would probably be negligible for short runs of triplex, particularaly as the voltage rises. It is significant in longer runs of overhead lines.
Is this a 34500 volt circuit?
respectfully

RE: Voltage Drop Formula

(OP)
Thanks for the responses so far.  The Mike Holt spreadsheets are informative but do not fully apply to my situation (limited due to the voltage level).  The voltage is 34500 (phase-to-phase).  The assumed PF is 0.9.  I was at the proposed site today and the length of the cable run is appoximately 1500 ft (one way).

RE: Voltage Drop Formula

The formula I use is I(Rcos theta + Xsin theta). If the distance is only 1500 ft you should not have any problem.

RE: Voltage Drop Formula

(OP)
Thanks for the responses and help.  The information you all have provided has been helpful and confirmed what I found.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources