Heat load Calc's

Heat load Calc's

Heat load Calc's

(OP)
In an electrical closet I have a 45, 75, 112.5(2) and a 150 kva transformers, 5 total. What figures do I use to calculate the heat gain for airconditioning? The room is 12 x 15.5 ft.

RE: Heat load Calc's

Jim:

I'm a mechanical so please bear with me!

Let's see 150kVA =~ 150,000 whatchamacallits = (about) 150kW.

1 kW = 3,412 BTUH (the Brits don't even use BTUs!!)

So 150 kW = 150 x 3,412 = 511,800 BTUH. Divide taht by 12,000BTUH/ton and youhave a heat gain of a whopping 42.6 tons! This is a whole lot of heat to pump outside if you consider that mechanical cooling in this size range can cost about $800/ton. Better to just ventilate the closet with outside air ... unless you're in the Saharah; but check the max allowable op temps of your trannys.

RE: Heat load Calc's

Hello

Transformer losses may average 7% for an older transformer, newer units may lose as little as 1-2%. For example, a 1500KVA unit running at a load factor of 65% and having an efficiency of 98% will experience a heat loss of about 13KW. If the load factor went to 85% the heat loss would be about 20KW. Typically today, a 25KVA unit should not lose more than 200W. I would estimate your losses to be in the range of 4 to 7 KW.

The NEC requires 100cfm of ventilation air for each KW of transformer loss. This assumes of course that the entering air temperature is low enough to "remove" your load.

I hope this helps you out.

RE: Heat load Calc's

Thanks, Fred .... I forgot: ALL that power IS going to heat; but NOT all in the closet. The wire "ducts" are taking it to the loads. So it's just a 2 ton load at 7kW of losses.  Ah well, it was late last night.

RE: Heat load Calc's

(OP)
Thank you both for your help. This will get me "in the ball park"

Jim

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources