(OP)
Where can I get some information on good plc I/O connection practice?  

My question is basically whether I should be connecting my I/O's to an isolated common or should the modules be independently common of each other?  

The reason I am asking is because I found that the (-) output 0-10Vdc signal from our VFD to our ControlLogix 5000 input module possesses an internal ground at the drive in which obviously is not an isolated common circuit.  

In addition, the PanelView Plus, that I had on the same isolated common, I found out has an internal ground, in which, the manual specifically states that there should not be any other grounds in the system for safety reasons, in other words, other than the PanelView's ground.

So this led me to beleive that maybe I don't necessarily need to be connecting all my I/O modules to a common common, I could just leave them independent of each other.  Is this true?

RE: All PLC I/O Common or Not

No, not as a general rule. Many manuals are a bit nebulous when it comes to grounds, signal grounds, earth, internal zero reference, chassis, screen ground - or whatever they are called.

Sometimes, there may be a need for a separate signal ground, but that signal ground is usually tied to common ground somewhere.

Keep it simple. And make sure you don't read more into the text than there is.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources