Trouble switching motor from VFD to line power

Trouble switching motor from VFD to line power

Trouble switching motor from VFD to line power

(OP)
Hello,
     I am trying to drive a 50 HP induction-motor pump alternately with a Yaskawa VFD, and line power.  What I am trying to do is to use the VFD to control the pump while the synchronous speed is less than 60 Hz.  When the synchronous speed reached 60 Hz, I use a set of reversing contactors which disconnect the pump from the VFD, and then connect it directly to the grid.  Sometimes this works fine.  The problem is that occasionally the connection to the line is very rough, and it results in popping a breaker.  It seems that the transition should be smooth.  I can start the motor directly from the line with no problem.  But when the VFD drops out and I try to connect from the line, I get the bump.  Any ideas why this would be happening?  And any ideas on how to fix it?

thanks,
Andrew

RE: Trouble switching motor from VFD to line power

Andrew,
It is highly likely you are out of phase with the motor. You could be 180deg out and this will lead to your breakers popping out. It is the same with a Star-Delta starter, the transition from Y-d can lead to the same result. Once you switch off to the motor and then back on, you are in no-man's land as far as the phase direction.
When you go from line power to your Yaskawa VFD, this will probably have a function called "flying Start" that will measure and 'catch' the motor without any of the problems you enounter going DOL. You can control the output from your VFD but DOL will simply provide full voiltage at 60Hz.

DOL=Direct on Line

RE: Trouble switching motor from VFD to line power

When the motor is disconnected, the magnetic field takes a little time to decay. If the motor is reconnected before the field decays, the field can be work to make the inrush current higher than it would be with a normal line start. The problem can be prevented by delaying closing one contactor by up to several seconds after opening the other. At 50 Hp, something like 1.5 seconds may be enough. Someone else here might have a better estimate. It is possible to synchronize the two power sources and use a quick or even closed transition, but that is difficult to do. I believe that even some who have done it successfully are not inclined to do it again.

RE: Trouble switching motor from VFD to line power

(OP)
Sed2developer,
     I have considered this situation.  But the motor is an induction motor, and so as soon as power is removed, there is no more field, and therefore there is no phase.  Am I incorrect about this?  I would assume that the disconnected rotor has no remaining induced current, and so it is simply free spinning.  Can you please explain why there would be a phasing to considered before connecting to the line?

thanks,
Andrew

RE: Trouble switching motor from VFD to line power

eeprom--

When you disconnect the motor from the VFD, it's still spinning AND the magnetic field has not yet decayed.  For a few cycles the motor is generating 3-phase voltage.  If you close the contactor with the motor's decaying three-phase voltage out of phase with the line supply, the end result is a very high current.  This is why your breaker trips.

The fact that it doesn't happen every time is due to the randomness of the situation's several factors.

old field guy

RE: Trouble switching motor from VFD to line power

(OP)
Thanks for the help.  This makes sense.

RE: Trouble switching motor from VFD to line power

Andrew
I should have added the part on that CJCPE and oldfieldguy have added.
There will be motor EMF and possibly opposite phase that will lead to a high short-circuit surge current. Pop.
The 1.5secs is about right. There will still be a surge as the motor gets back to rated speed but nothing like going DOL or trying to reconnect too quickly.

RE: Trouble switching motor from VFD to line power

The motor field will take some time to decay. I would expect a 50hp to require around 0.5 seconds for the terminal voltage to decay. I have seen larger motors (100's of HP) require 1.5 to 2 seconds.

A wye-delta starter can be built with resistors. The resistors are connected first during the transition to "pull" the motor into phase with the power system. Then, the main contactor is closed. I know at least one chiller manufacturer that requires their wye-delta starters to be closed transition because an open transition damages the chiller.

Maybe you could do something similar here?

RE: Trouble switching motor from VFD to line power

eeprom; What you're doing is guaranteeing that you will be randomly popping breakers or something worse eventually.

Why are you using a VFD?  If you don't need the 'V' you should probably just change to a soft-starter as they usually deal with the contactor transition automatically.

  Generally pumps are nice things to start DOL.  Do you have voltage sag problems if you go that way?

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: Trouble switching motor from VFD to line power

I agree with the opinions above. The induction motor becomes a generator for some cycles after the power supply is disconnected. Out of step voltage reconnection develops high currents and mechanical stress surges.
A time delay will allow dissipating the residual magnetism and generated voltage, and the resultant transient.
To avoid the reconnection current surge due to high slip of the motor speed,  increase the VFD frequency a little bit over 60 HZ before the VFD is disconnected, that way the motor speed will be still close to 60 HZ synchronism when the main supply is connected.
In my opinion 0.5 seconds delay (30 cycles) is more than enough to dissipate any residual voltage. Remember that the pump is loaded and the speed will drop sharply when the electric power is removed, since the pump inertia is normally light.

RE: Trouble switching motor from VFD to line power

aolalde makes a good point. Too long of a delay will allow the motor to slow down enough so that when reconnected X-line, there will be a significant inrush current again, along with the associated torque spike. In my work on DC injection brakes where we had the same issues, we found that the field decay time on motor designs under 100HP was approximately 28ms. But to that you must add the reaction and opening time of the contactors, which can range greatly from brand to brand. For example, ABB contactors that size take up to 130ms to open. Then you add in the closing time for the X-Line contactor of around 80ms and you start to approach 1/2 of your .5 second delay already. So I recommend a delay that is .25 sec., then allow the mechanical issues to do the rest. Any longer and you risk a re-close spike that will damage your equipment.

As an aside, this subject has been dealt with extensively by VFD manufacturers in what are called "synchronous transfer" bypass systems, originally promoted by Robicon drives for years MV systems and taken up by several other manufacturers now on both MV and LV drives. Yaskawa just doesn't happen to be one of them. In a sych. transfer system, the line sine wave is monitored and the VFD output is synchronized to it and both systems are connected in parallel. But a reactor is put into the VFD side during parallel operation to prevent damage to the transistors. Not something I would tackle without experienced help however.

RE: Trouble switching motor from VFD to line power

I suppose the easy fix is to not bypass. What's gained by bypassing?

RE: Trouble switching motor from VFD to line power

that last point is valid, I want to know what is the purpose in bypassing the vfd after startup?  

RE: Trouble switching motor from VFD to line power

In my experience it is typically done so that the VFD can be reused for an adjacent pump. The extra contactors and SCPD to do the bypass correctly are less expensive than the additional VFD(s), especially as you get to have more and more pumps. I have seen this done for as many as 5 pumps and one VFD. Theoretically there is no limit to how many you can do but at some point the extra control gear to do it makes it uneconomical compared to buying another VFD. There is also the issue of a lack of redundancy to consider. But I did one job where we put in 3 VFDs for 9 motors, it was less than 1/2 the cost of 9 VFDs. It's a trick often used when budgets are tight, but it is also fraught with pitfalls for the inexperienced.

It's also done sometimes when the full speed run time grossly exceeds the variable speed run time, or the VFD is used just as a soft starter for extremely weak systems where a regular soft starter will not adequately reduce starting current, i.e. 1.0 - 2.0 x FLA situations. To leave the motor on the VFD for long periods of time at full speed means suffering the energy losses in the VFD.

RE: Trouble switching motor from VFD to line power

(OP)
Yes, this is correct.  The system I am speaking of has three pumps.  When the system comes on line, there is only one pump.  If that pump reaches full speed and the line pressure is still too low, pump 1 is connected across the line, and pump 2 is then connected to the vfd.  Pump 2 then becomes the control pump.  This system is less expensive than 3 vfds.  However, we are running into problems in trying to get the pumps to switch from vfd power to the grid.  

RE: Trouble switching motor from VFD to line power

Admit it you're also having trouble actually getting the control pump to 'control' too...   ?

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: Trouble switching motor from VFD to line power

One trick that has worked for me in the past is to do what aolalde said in his post; slightly overspeed the pump right before transfer, maybe 5% or there about. Then when you go into open transition and it coasts for that 1/2 second, it is closer to normal speed when reconnected. Tricky to get right however, takes some trial and error which can be hard on your system.

But then again you already have that condition now so it can only get better. (famous last words)

RE: Trouble switching motor from VFD to line power

Why don't you just run with two fixed speed pumps and one variable? With a bit of simple logic that would give you a controllable output over the full range from zero to three pumps flat out.
 

----------------------------------
  Sometimes I only open my mouth to swap feet...

RE: Trouble switching motor from VFD to line power

ScottyUK,
The usual reason is the same for any triplex or duplex pumping station; alternation of the pumps to avoid excessive wear and tear on any one pump, plus complete redundancy. It's the same reasoning behind not just doing it with one big pump.

It's a big deal to the pump people. I'm working on a triplex system design right now (non-VFD) where we are using kWh and cycle counts on each pump to feed back into a PLC. The PLC then determines a more complex alternation scheme based on cumulative motor heating and damage curves from excessive starting during wildly variable flow conditions. It will also allow the system to revert to a full duplex if any one of the 3 pumps goes down, then a full simplex if only one pump is alive. When pumps are then fixed and returned to service, the PLC will then rebalance the service time.

RE: Trouble switching motor from VFD to line power

Hi Jeff,

Yes, that makes sense.
 

----------------------------------
  Sometimes I only open my mouth to swap feet...

RE: Trouble switching motor from VFD to line power

Learning from this.

Gunnar Englund
www.gke.org
--------------------------------------
100 % recycled posting: Electrons, ideas, finger-tips have been used over and over again...

RE: Trouble switching motor from VFD to line power

Jeff; What kind of application is that(effort) for?

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: Trouble switching motor from VFD to line power

Keith,
The most common is a pump station, such as a lift station for a wastewater system or a pressure booster for a water delivery system. Because of the nature of the beast, the flow or pressure requirements can be extremely variable.

RE: Trouble switching motor from VFD to line power

Going back to the original poster, assuming the 3 x pumps are feeding into the same system, I can't quite work out why you would want to switch the VFD from one pump to the next.
Within our VFD, and it is similar to a number of drives on the market, there are functions called "motor staging" or "Pump Staging".
This method would operate with the VFD using it's internal PID loop and the pressure transducer feeding back to the VFD the PID FB. Scenario is this:
Pump 1 is connected to VFD directly, no switching required between VFD and motor. The VFD starts Pump 1 and runs in a PID closed loop controlling pressure. As pressure increases then the VFD pump slows down, as the pressure drops then the VFD increases pump speed to try and maintain pressure SP. If the SP cannot be reached and Pump1 is running flat out, then an internal timer will kick in within the VFD. After a minute or so of running flat out and still not reaching required pressure, an internal relay will change state and bring in Pump 2.
Pump 2 will be operated either DOL (Direct on Line) or via a Y-d starter or a softstarter. At the moment the relay on-board the VFD was to bring in the Pump 2 then it would momentarily drop in speed, cut out the PID loop to try and eliminate a large in-rush as the fixed speed pump was brought in. This is the difficult part and one that generally needs the most 'fine tuning'.
The position now is that Pump 2 is running at full speed and Pump 1 would typically be running quite slow (the PID is now back in operating). The feedback from the pressure transducer is providing the VFD with the pressure demand and again, if the pressure is still lower than the SP then the VFD increases the speed of Pump 1. If the same scenario happens with pressure dropping and Pump 1 running at full speed, then the 2nd relay on the VFD will bring in Pump 3 (again, at fixed speed). Pump 1 would have dropped off to try and compensate for the surge.
Now with P1 varying and P2 & P3 at fixed speed, you will have a system that should be designed to full capacity and cope with the worst case scenario in pressure drops.
If the pressure starts to rise and the P1 is running at minimum speed, then the opposite process will operate with P3 being taken out of service with the Rly onboard the VFD and so on.
This is a typical Pump Stage process that a large number of VFD's on the market can function with all the logic on-board the VFD.

This system would not necessitate the need to bring in and out the output stages of the VFD and potentially lead to the problems originally explained.
Hope this makes sense.
 

RE: Trouble switching motor from VFD to line power

sed2,

This is more-or-less what I was alluding to in my earlier post. Seems these pump guys like the facility to allow any of the pumps to be assigned to the function of P1, P2, P3 in your example in order to balance running hours. That makes things a little trickier.
 

----------------------------------
  Sometimes I only open my mouth to swap feet...

RE: Trouble switching motor from VFD to line power

sed2developer,
I agree that is the most commonly applied application as far as VFD manufacturer's built-in drive control macros, but there are a lot of engineers who will not use it. The reason (besides the "difficult part" you mentioned) is that Pump #1 ends up with a lot more running time than the others because it cannot be included in the alternating scheme since it is the only one on the VFD. Granted, being on the VFD means the pump is not being worked as hard, but things like seals and bearings wear out based on run time as well. I did a quadraplex system several years ago and the VFD driven pump now has around 7 times the running hours as the other 3. The risk is that it wears out faster and when it fails or is taken out of service for maintenance, they have now lost almost all of their system control.

RE: Trouble switching motor from VFD to line power

ABB supplies a "Pump/Fan Macro" in their 550 and 800 series drives.  The operation is as described above with one pump being variable speed and the others on contactors.

You get the choice of operating the system that way or with pump rotation.  Pump rotation periodically moves the lead and variable speed control to the next pump.  After a fixed number of operating hours, the rotation is to the next and so on until all have about the same hours.

You need one drive sized for the pump motor hp and two contactors for each motor---one to connect the motor to the line and one to connect to the VFD.  The drive logic takes care of the sequencing and rotation leaving only the contactors to be added.

I've done one of these in a hospital water supply system and it works really nicely.  You can even take one pump off line and the sequence and rotation will jump over that position and just keep on working.

Very nice!

RE: Trouble switching motor from VFD to line power

(OP)
Two main concerns of this design are that the pump run times remain balanced, and that we don't cause water hammers by bringing auxiliary pumps online too abruptly.  Turning on the auxiliary pumps has been a bit of a trick.  A soft-start for each motor would be nice, but the system is already built and paid for.  And three soft starts would be a significant cost.  One idea proposed has been to bring auxiliary pumps online by first dropping the VFD to a fixed setting corresponding to about half flow.  With the lead pump running at half flow, we can start one of the auxiliary motors straight off the line.  As soon as the contactors for the second motor are closed, we put the VFD back into control mode.  The result should be a minimal water hammer.    

RE: Trouble switching motor from VFD to line power

That's interesting Dick,

Is there an application note on this scheme anywhere? A ready built macro would save a lot of engineering time - I'd like to have a look at this one.
 

----------------------------------
  Sometimes I only open my mouth to swap feet...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources