FANS IN PARALLEL INSTALLATION

FANS IN PARALLEL INSTALLATION

FANS IN PARALLEL INSTALLATION

(OP)
IF TWO FANS ARE IN PARALLEL INSTALLATION, IS IT NECESSARY TO PRIVIDE BACKDRAFT DAMPERS ON THE DISCHARGE SIDE OF EACH FAN IF THEY ARE START UP AND SHUT DOWN AT THE SAME TIME? IF NOT,DO THE FAN CAN BE DEMAGED WHEN THEY ARE START UP OR SHUT DOWN IN SERIES?
THANK YOU

RE: FANS IN PARALLEL INSTALLATION

Yes, squared.

RE: FANS IN PARALLEL INSTALLATION

They wont be damaged but the absence of a back draugh damper will result in leakage and reduce the fan overall flow rate when only one is running

RE: FANS IN PARALLEL INSTALLATION

I disagree that they won't be damamged remp.

If you don't have a backdraft damper then you will have airflow spinning the fan backward. When the fan goes to start it will have to start against the backward momentum.

This does very bad things to the motor and belts.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources