pilot psv in steam service with 'condenser' on pilot line
(OP)
Hello,
We have a pilot psv on a superheated 600 psig steam line. We operate close to the set pressure of the psv, hence a pilot psv was selected.
We were told by the vendor that the maximum temperature the o-rings, etc... can handle is around 400 F. Therefore, there is a condenser on the pilot line which radiates to ambient atmosphere to try and cool the steam to a suitable temperature.
The psv is located outside.
We are wondering if anyone else has used something similar, and could share their experience.
Best regards,
Jonathan
We have a pilot psv on a superheated 600 psig steam line. We operate close to the set pressure of the psv, hence a pilot psv was selected.
We were told by the vendor that the maximum temperature the o-rings, etc... can handle is around 400 F. Therefore, there is a condenser on the pilot line which radiates to ambient atmosphere to try and cool the steam to a suitable temperature.
The psv is located outside.
We are wondering if anyone else has used something similar, and could share their experience.
Best regards,
Jonathan





RE: pilot psv in steam service with 'condenser' on pilot line
If you do not already have checked this out, I also believe pilot oprated systems exists with steam condensation and in addition a membrane separated secondary clean pilot fluid circuit to operate the pilot without impurities influencing the operation.
I am a bit unsure about the present status and construction availability, but you could try Weir with the French Sarasin-RSBD pilot operated PSVs supplied after European Atomic Power-plant safety requirements.
RE: pilot psv in steam service with 'condenser' on pilot line
Was the psv used in outdoor service?
Regards,
Jonathan
RE: pilot psv in steam service with 'condenser' on pilot line
What we are most concerned about is potential freezing. Our ambient temperature can drop to about -20F.
Did you have any problems with freezing?
Many thanks.
Jonathan
RE: pilot psv in steam service with 'condenser' on pilot line
The valve is a Dresser 3900 modulating pilot series, with a 2900 series heat exchanger installed on the pilot line.
Thanks in advance to any help provided.
Regards,
Jonathan