Has anyone heard any information regarding a utility steam pipe failure in Kansas?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Steam Pipe Failure
RE: Steam Pipe Failure
RE: Steam Pipe Failure
http://www.kansascity.com/206/story/100971.html
RE: Steam Pipe Failure
-failure was in the feedwater piping to the attemperator station
- the feedwater line was reported to be 4" Sch 160, SA 106 Grade C carbon steel
- cause of failure was flow accelerated corrosion (FAC)
- 18" long rupture
- piping adjacent to the failure was reduced to 0.100"
RE: Steam Pipe Failure
rmw
RE: Steam Pipe Failure