3 pole or 4 pole STS??
3 pole or 4 pole STS??
(OP)
Hi,
Can someone clarify for me...when can we select a 3 pole STS over a 4 pole STS unit?
Thanks
Allan
Can someone clarify for me...when can we select a 3 pole STS over a 4 pole STS unit?
Thanks
Allan






RE: 3 pole or 4 pole STS??
RE: 3 pole or 4 pole STS??
When dont you need to switch the neutral??
RE: 3 pole or 4 pole STS??
RE: 3 pole or 4 pole STS??
I am to install a STS (static transfer switch), in the upstream we only have one supply and one generator...I am planning to use a 3 pole STS instead of a 4 pole STS...(since we dont need to switch the neutral because there is only one generator)...Am I right?
Please advise
RE: 3 pole or 4 pole STS??
My preferred installation is as follows:
Supply to 3 pole transfer switch.
Generator to 3 pole transfer switch.
Solidly connected neutrals.
From the transfer switch to the main panel.
One connection from neutral to ground in the main panel.
The code only allows one connection from the neutral to ground. There are very good reasons for this.
If for any reason, there must be more than one ground on the neutrals then the neutrals must be switched in such a manner that only one at a time is ever connected.
There may be some exceptions to the "one ground connection" rule if more than one building is involved.
respectfully